Thread: 3 Phase Question
-
30th April 2007, 10:06 AM #1Novice
- Join Date
- Apr 2007
- Location
- Townsville
- Posts
- 9
3 Phase Question
I am currently doing a long term reno on my house, which has 3 phase power to drive my ducted air con.
My mains are 63amps, and according to the electrician he has spread the house over all three phases.
My question is given that many new houses are apparently 100 Amp. Is there any point in me attempting to upgrade my mains? I believe that the cable running to the house is 16mm (?? - which would have to be replaced in order to go to 100 amp?).
Am i getting any advantage here by having three phase? If so what?
Am I getting potentially 63 Amp on each phases therefore negating any need to go to 100 amp?
-
30th April 2007, 02:57 PM #2rrich Guest
How much current do you expect to use at one time. If that mumber if over 63 amps on each of the phases (all at the same time) then you may need to upgrade.
BTW - During a remodel or our home, I added a 100 amp sub-panel to the shop (errr garage) with a like upgrade to the main panel to 200 amps and my local utility didn't think that increasing the size of the mains (house to pole) was necessary. I have run the cabinet saw and dust collector while SWMBO was cooking (electric oven and electric cook top) with the A/C running. Not a big deal. Although I think that if the clothes dryer was electric and also running there might be a problem with the main tripping.
-
30th April 2007, 03:07 PM #3
You have already answered your first question - you can run three-phase equipment such as a 3-phase air conditioner.
If you have 3 phase at 63 amp per phase, it is the equivalent of 3 x 63 = 189 A single phase. It is hardly worthwhile going to 100A single phase (which is what most new houses would have). You would have to have an awful lot of electrical stuff to need 100A 3-phase supply.
-
5th May 2007, 11:13 PM #4Member
- Join Date
- Dec 2006
- Location
- Brisbane
- Posts
- 44
Just to clarify what crisp said,
You have 63 amps available per phase, not 189 amps single phase. If you are mainly running single phase items in your garage, ensuring that the load is spread over the three phases in the shed, you wouldnt need 100amps per phase for your property.
If you are worried about the load being drawn in the shed, spread the load over the seperate phases. Im assuming you have 3 phases in the shed?
Cheers
Steve
Similar Threads
-
Ducted air off single phase? or do I need 3 phase?
By mixin in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etcReplies: 5Last Post: 2nd April 2007, 11:28 PM -
3 phase at home
By Com_VC in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etcReplies: 6Last Post: 22nd August 2006, 04:21 PM -
Two-part Question
By Rodgera in forum JOKESReplies: 1Last Post: 12th May 2006, 07:17 PM
Bookmarks