Current, wattage, HP and 3 Ph motors
Hello all,
I have a 3 phase variable speed (frequency) motor that I have waiting for a project. Question is, to work out the wattage of the motor is it the same as for a single phase electric motor as in Volts x Amps = Watts, then divide by 746 for horsepower?
The spec plate says it draws 6 amps, so does that mean about 1400 watts and just shy of 2 HP?
Cheers,
Simon
-
15th March 2012, 08:03 PM #2
Pink 10EE owner
- Join Date
- Aug 2008
- Location
- near Rockhampton
- Posts
- 4,298
6 amps per phase?
Light red, the colour of choice for the discerning man.
-
15th March 2012, 08:09 PM #3
GOLD MEMBER
- Join Date
- Aug 2011
- Location
- Melbourne
- Posts
- 2,947
-
15th March 2012, 08:11 PM #4
Hi,
Your voltage should be 440 so 6 amp would be 2640w.......
Ewan
-
15th March 2012, 08:13 PM #5
But after your last reply thats more than 10 amp.....
-
15th March 2012, 08:26 PM #6
GOLD MEMBER
- Join Date
- Aug 2011
- Location
- Melbourne
- Posts
- 2,947
-
15th March 2012, 08:26 PM #7
What else does the spec plate say? Treadmill motors are often non standard with a special VSD to control them. My treadmill motor is 2HP but it is 240V DC I think.
Edit: too slow
-
15th March 2012, 08:29 PM #8
GOLD MEMBER
- Join Date
- Aug 2011
- Location
- Melbourne
- Posts
- 2,947
The only reason the motor is 3 Ph is because they use a dedicated VFD to vary the speed of the treadmill. Some treadmills use a DC motor and vary the duty cycle by PWM but this one uses a 240 V 3 Ph motor and a VFD.
Cheers,
Simon
-
15th March 2012, 08:32 PM #9
I make it 3HP.
E x I x root3 x power factor
-
15th March 2012, 08:33 PM #10
Are you sure it's a three phase induction motor, it's not brushless DC by any chance?
I can't see a treadmill having a 415 V 3 phase induction motor, but who knows?
There should be a name plate, if not some other identification.
Regards
Ray
PS... Seems like there were 3 or 4 posts while I was typing, 240 x 6 x 1.732 x 0.85 = 2.2 kw 3 hp it is..
-
15th March 2012, 08:35 PM #11
I would say your 2hp would be right then.
Never thought of treadmill motors as good speed controlled motors. Oh dear something else to look out for. Mind you, DC would be great with PWM (now you speakin my language) and feed back as you can still get close to full power at low revs.
Ewan
-
15th March 2012, 08:35 PM #12
Senior Member
- Join Date
- Oct 2011
- Location
- Brisbane
- Posts
- 83
-
15th March 2012, 08:46 PM #13
GOLD MEMBER
- Join Date
- Nov 2007
- Location
- melbourne australia
- Posts
- 2,585
Something's not right here. 3400W is a HUGE amount of power for a treadmill. In any case, you wouldn't be able to plug it into a 10A GPO if it drew 3400W.
I also tend to think it might be a brushless DC motor.
-
15th March 2012, 08:49 PM #14
Tools4me assumed like i did, that is 415v, but its only 240, so if you pop that into the calculations you get 1992w, but i'm not sure if the PF would be the same.
Hmmm i think the only sure thing is that you have a motor.
You don't have one of those power meters that you plug in do you? you could plug it into one and run it on full to see what the draw is.
Ewan
-
15th March 2012, 08:54 PM #15
Tools4me,
Am i right in thinking that to work out any 3 phase wattage you use the square root of the no of phases? So it a motor is running on, oh god brain failure, delta? only, you would use the square root of 2 (i think i'm right in thinking that a motor in delta only uses 2 phases, star is 1 and star/delta is all three)? I know plenty about DC and single phase, but three phase is, well, 3 times as complicated.
Ewan