    Default Hot Water Pressure

    I have recently had renovations done at my house, and the hot water was converted from a Gravity feed with tank in the ceiling, to a Mains pressure Hot Water Service mounted under the house, in the same location as the old Hot Water Heater.
    the problem is the hot water pressure is no better than it ever was with teh gravity feed system, and in some rooms it is worse.

    Because it is so bad, it takes an age to heat up at the taps and continues at a very slow rate.

    I have a tempering valve installed at the cylinder, as well as shut off valve ( i dont know the proper name for it).
    i was wondering if these may be the problem, or could it be the pipes.
    Im not sure the diameter of the piping, but it was NOT replaced from teh gravity feed system, and i am dubious about the quality and diameter.
    in fact, the only NEW piping installed to a vanity in the new bathroom, has poor cold water pressure as well, and the hot at that sink is barely a trickle. all the plumber did was replace all the threaded joins with solder joins and replace the pipe from under the house up the walls to the fittings, so all the pipework behind new plaster is new for the hot and cold pipes. but under the house, he left the old copper pipes for the hot water, and galvanised pipes for cold water that he simply joined onto whereever the pipes went into the walls to fittings.

    THe builders have since stopped talking to us, and they have not paid any of their subcontractors, such as the plumber, so nobody will come back to look at it.


    i have already checked the taps mixer filters, and they are fine. the cold water pressure everywhere aside from teh vanity, is quite good, but the hot is really really slow.

    as a rough guide, Once the water is hot from the taps (which takes a good minute or so), it took about 29 seconds to fill a 1L container with pure hot water. so a flow rate oof only about 2L per minute roughly i would say. and that was at the kitchen where the flow is best.
    in the laundry, which is farther away from the HWC, it took closer to 38 secs for a 1L fillup. and the vanity takes nearly a full minute to filla Litre.

    Any advice would be welcomed, ideas on whether there is anything i can check myself, filters etc??

  2. #2
    Join Date
    Aug 2003
    Location
    Pambula
    Age
    59
    Posts
    5,026

    Default

    Not a plumber but I know that pressure reducing valves are now fitted to all new hot water systems.
    "I don't practice what I preach because I'm not the kind of person I'm preaching to."

  3. #3
    Join Date
    Jan 2008
    Location
    Hobart, Tasmania
    Posts
    17

    Default

    I dont think mine has that. the only fittings on the outlet side is the tempering T-piece and a stop valve with a small black dial that will completely shut off the hot water supply to the house, out of the cylinder.

  4. #4
    Join Date
    Aug 2003
    Location
    Pambula
    Age
    59
    Posts
    5,026

    Default

    It would be on the inlet side - it's designed to stop the cylinder exploding from too high mains pressure. I have a vague recollection that there is also a pressure reduction device in the tempering valve on the outlet side too. Some little plastic thing that fits into the outlet.

    As far as I know, these things are required by law now in NSW.
    "I don't practice what I preach because I'm not the kind of person I'm preaching to."

  5. #5
    Join Date
    Feb 2008
    Location
    Sydney
    Posts
    66

    Default

    you say you have sections of old gal pipes?, does any of this feed to the hot water system & basin? as gal rusts inside eventually to the point a drop will be lucky.
    Tempering valves do have strainers in the hot & cold inlets.
    The pipe sizing, should be ok , usually gravity fed systems are a 3/4 outlet that have 5/8 drops.
    have you checked the aerators on the sink spouts aswell, not that that will be the main prob, but if you have different pressure, you may have a few clogged aerators.

  6. #6
    Join Date
    Oct 2007
    Location
    Hobart
    Posts
    139

    Default

    1. Have you measured the flow from a cold tap? If so, how many litres per minute?

    2. Have you checked that the inlet valve to the water heater is fully open?

    Also, does the flow drop noticeably with only a slight turn of the valve down from full? It normally shouldn't but might if the valve is a dud.

    3. I assume that the mains pressure HWS is a storage tank? Or is it instant type?

    4. If it's a storage tank, operate the relief valve (open and close it GENTLY or you'll break it). How good is the flow from the pipe coming from the valve? (Ideally measure it).

  7. #7
    Join Date
    Jan 2008
    Location
    Hobart, Tasmania
    Posts
    17

    Default

    Cold Water from the kitchen tap is about 8seconds per litre, so thats about 7 - 7.5 L/minute.
    the hot is more like 2 L/minute if i am lucky.

    The inlet valve to the heater is turned open as far as the small black dial will turn, so i assume it is fully open.

    I will check the slight turn theory.

    It is a 240L storage tank. the relief valve, do you mean the lever style on the opposite side of the tank, which runs down to an overflow style pipe?

  8. #8
    Join Date
    Feb 2008
    Location
    Sydney
    Posts
    66

    Default

    thats the one

  9. #9
    Join Date
    Jan 2008
    Location
    Hobart, Tasmania
    Posts
    17

    Default

    ok, i will check that one tonight.
    it does flow a reasonable amount out of hte overflow pipe everyday, i noticed on the weekend. not a constant flow, but a fair amount of water over the day drips out onto the ground from the overflow pipe.

  10. #10
    Join Date
    Oct 2007
    Location
    Hobart
    Posts
    139

    Default

    What I am trying to work out, by checking the relief valve maximum discharge rate when open, is whether the problem is on the inlet or outlet side of the hot water cylinder plumbing. That is, not enough can get in? Or it can get in but can't get out through the hot water pipes around the hose? Knowing that will narrow the range of possibilities as to what's wrong.

  11. #11
    Join Date
    Jul 2007
    Location
    Sydney-south
    Posts
    333

    Default

    Mate if the relief valve dumps with as much or nearly as much pressure as the cold water then it may be in the HW pipework where you will find your problem.
    Plumbers were around long before Jesus was a carpenter

  12. #12
    Join Date
    Jan 2008
    Location
    Hobart, Tasmania
    Posts
    17

    Default

    i havent had a chance to test this yet, but i did notice wheni moved a pile of rubbish from outside the house yesterday that the ground is VERY VERY wet and the relief valve pipe trickles almost constantly.
    should it be plumbed into a drain or something? at the moment it simply runs through the wall from under the house and drips into the dirt outside my house. for about 50cm all around, the ground is quite damp.

  13. #13
    Join Date
    Jul 2007
    Location
    Sydney-south
    Posts
    333

    Default

    That would mean the reief valve needs replacing for a start.
    Plumbers were around long before Jesus was a carpenter

  14. #14
    Join Date
    Jan 2008
    Location
    Hobart, Tasmania
    Posts
    17

    Default

    ok, i am getting a couple of plumbers out to give quotes to check it out and fix the hot water situation.
    we also discovered yesterday that the toilet pan is leaking, and trickling water out from underneath everytime we flush.

    This is just never ending.

    Anyy recommendations on a good plumber in Hobart, Tas?

  15. #15
    Join Date
    Jan 2008
    Location
    Hobart, Tasmania
    Posts
    17

    Default

    My Hot water pressure problems are now fixed.
    Yesterday we discovered a leak around the toilet Pan, so called a plumber in to fix that.
    i mentioned to him that the hot water pressure was bad and he went under the house, saw that we had a NEFA brand Pressure Limiting Valve and said he would 99% guarantee that was the problem. He told me that about 1 in 5 of the NEFA brand valves fail and they dont use them anymore.

    so he replaced the valve, and hey presto we have pressure!!!!
    as for the vanity tap which had poor pressure on hot and cold, I removed a small O-ring from the filter on the tap and it now works perfectly!!

    Thanks to all who replied, i am releived it was something so simple and cheap to fix!!!

Similar Threads

  1. hot water pressure
    By ledwards in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 8
    Last Post: 18th August 2007, 08:00 PM
  2. Hot Water, no pressure after rainwater ran out
    By timgrigg in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 3
    Last Post: 19th March 2007, 09:20 PM
  3. Water pressure really low - new house
    By jmtheo in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 7
    Last Post: 19th September 2006, 03:34 PM
  4. Hot Water Pressure Problems
    By DarrylF in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 6
    Last Post: 5th July 2006, 11:10 AM

Tags for this Thread

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •