Joining load bearing beams
I am wanting to get peoples ideas here....still in a high level planning phase.
One idea SHMBO has is to remove two internal load bearing walls that join at 90 degrees to each other. I can understand the princple of placing appropriatly sized beam for one of the walls, but I cannot get it clear in my head how the second beam would attach.
would I install one appropriately engineered beam in then install the second beam mid section to the first higher into the roof space?
The spans are reasonably sized, one being 6 metres and the other 4 metres.
-
5th December 2005, 03:08 PM #2join at 90 degrees to each other
If you want it to be clear underneath, then the beam that is intersected by the other will need to carry half the weight of the intersecting beam, as well as it's own load. Sounds like a job for an engineer. I'm sure there's a hanger arrangement or something that would allow you to have both beams at the same level. You might have to go to steel."I don't practice what I preach because I'm not the kind of person I'm preaching to."
-
5th December 2005, 03:19 PM #3
Yep spot on...they would join like a T.
I was thinking the steel option would be the only way.
Got any rough ideas on expence...$1000?
-
5th December 2005, 03:31 PM #4
Work on aobut $4000/ton for structural steel. Add the engineer's fee, freight, and erection time.
The only way to get rid of a [Domino] temptation is to yield to it. Oscar Wilde
.....so go4it people!
-
5th December 2005, 04:28 PM #5
When you say it's load bearing, what is actually sitting on it? Could you reposition some of the roof timbers to free up the intersecting wall? Then you could get away with one structural beam. There might an under-purlin strut on the top plate that could be moved or maybe a strutting beam could be put in to span the old wall.
"I don't practice what I preach because I'm not the kind of person I'm preaching to."
-
5th December 2005, 06:15 PM #6
Timber span tables do list dimensions for beams and strutting beams which you may be able to apply to your situation.
-
5th December 2005, 07:33 PM #7Hammer Head
- Join Date
- Jan 2005
- Location
- Sydney
- Posts
- 191
whats the walls holding up.
first floor joists
roof and ceiling
trusses
stick frame
-
5th December 2005, 07:36 PM #8Registered
- Join Date
- Aug 2003
- Location
- .
- Posts
- 4,816
I think you prolly need to speak to an engineer.
Al :eek:
-
6th December 2005, 08:40 AM #9
Thanks for the tips.
Will be off to an engineer if we plan on using that particular design.
cheers
-
6th December 2005, 10:49 AM #10Intermediate Member
- Join Date
- Nov 2005
- Location
- Brisbane
- Posts
- 26
Originally Posted by jimc
Also bear in mind that each beam will need to be supported at each end on triple studs or similar and that this load concentration needs a load path to get to ground if you are not on a floor slab.
-
6th December 2005, 11:29 AM #11Also bear in mind that each beam will need to be supported at each end on triple studs"I don't practice what I preach because I'm not the kind of person I'm preaching to."
-
6th December 2005, 12:51 PM #12Novice
- Join Date
- Oct 2005
- Location
- Ringwood Vic Australia
- Age
- 57
- Posts
- 3
Sounds like my place.
Steel beam (250 x 90 C 36 PFC)with bracket welded at required intersection, supported by triple studs at each end. Intersecting timber beam (2/240 x 45 F17 KDHW nailed together) bolted to welded bracket and supported by triple studs at other end.
If its a larger ceiling I would sugest also using metal battens for your plaster, you will get a better finish.
Cheers
Marty
-
6th December 2005, 12:56 PM #13Novice
- Join Date
- Oct 2005
- Location
- Ringwood Vic Australia
- Age
- 57
- Posts
- 3
I should of mentioned the bracket gets welded to the inside of the channel and the timber beam gets morticed to fit same.
I hope this helps.
Cheers
Marty
-
6th December 2005, 01:43 PM #14Intermediate Member
- Join Date
- Nov 2005
- Location
- Brisbane
- Posts
- 26
Originally Posted by silentC
-
6th December 2005, 02:25 PM #15
thanks for the help...
ok details as follows....
roof size - 24m and terracotta roof tile
it is only going to support roof and ceiling load
the larger beam needs to be at least 5.7 metres long with the intersecting beam 2.5 metres along its length.
the intersecting beam needs to be at least 4.3 metres long
Can 100*75 RHS be used as a structural member?