Page 1 of 4 1234 LastLast
Results 1 to 15 of 59
  1. #1
    Join Date
    Mar 2008
    Location
    Perth
    Posts
    6

    Angry Roof framing standards - new house

    Hi all,

    I'm currently building a double brick home with timber roof frame and colorbond roof cover in Western Australia. The roof has recently gone up and there is something I'm particularly not pleased with. I've been searching for answers and came across this forum and would appreciate the advice of anyone who might be in the know here, particularly with respect to the building codes.

    Refering to the attached pictures you can see a heavy steel "I" beam supported at either end by a stack of four loose bricks on top of the timber roof plates. The walls supporting all this is a single leaf internal brick wall (10cm). The diagonal 'braces' were added by the builder after I told them I was unhappy with the steel beam just sitting on the stacked bricks...

    The builder has told me this is fine (prior to the 'braces' being added). I've had an independent building inspector in who also told me it is ok (prior to the 'braces' as well). And I've recently spoken to someone at Archicentre, after sending them these images, but they were quite vague and said the building codes are also not specific in this area. His main concern was on the bearings being sufficient.

    This type of thing appears to be common practice in Western Australia which I find quite astounding. Other people I've conversed with over here have seen similar and been told the same by the builders. I had expected the building inspector to be shocked by it but he practically ignored it for other issues. Unfortunately it seems I have little choice but to accept it at this point...

    I'd appreciate some informed advice, particularly with respect to Australian Building Codes.

  2. #2
    Join Date
    Oct 2007
    Location
    Seven Hills, NSW
    Posts
    159

    Default

    A few things to make sure of:

    The stud wall has adequate studs under the beam location.
    The steel beam is tied down to the wall frame.

    It does look messy but as long as there are no lateral loads on the beam, it will stay in position. I would be more worried about the uplift forces not being catered for than the bearing of the beam.

  3. #3
    Join Date
    Feb 2003
    Location
    Garvoc VIC AUSTRALIA
    Posts
    3,208

    Default

    Of course you could pay more money and get the builder to support it some other way

    You've been told its standard building practise by your own experts

    Its Customers like you who make me very happy that I'm retired
    Regards, Bob Thomas

    www.wombatsawmill.com

  4. #4
    Join Date
    Mar 2007
    Location
    Adelaide South Australia
    Posts
    76

    Default

    arc,I can't make out what the steel beam is supporting.

    If it is a live load or supporting a roller door then I would be worried as the vibration could over time cause the bricks or beam to move.

    Personally I would prefer to see a timber stub wall under the beam with the whole lot strapped or bolted down to the wall below as expressed in the other post to resist uplifts.
    Don't force it, use a bigger hammer.

    Timber is what you use. Wood is what you burn.

  5. #5
    Join Date
    Jun 2007
    Location
    Perth, WA
    Posts
    67

    Default

    You have posted this exact same question on another forum and you got baised information by a bunch of wannabies who dont know there a*s from their face so now you are concerned

    1: Your roof is fine, it will not fall down by itself, the bits of timber dont do anything but might make you feel better. Nice of the builder to humour you. I would have told you to stick it.

    2: You have had it independantly inspected and it passed no probs

    3: the beam is not the sole item holding your roof together, it quite possibly has no significant structural load against it anyway.

    4: ideally it would be best sitting on 1 brick instead of 4, but this isnt the case and wont change

    5: it appears you just posted here to have a whinge, as you said yourself you cant do anything about it anyway

    Seeing the walls are solid brick the beam obviously has sufficent support from below.

    Supply some photos of anything the beam is supporting and maybe my opinion will change, but for the moment my suggestion is to stop stressing about it and move on in life.

    This is not opinion, this is fact, and you need to look at the facts not everyones personal thoughts (saying "I wouldnt be happy with it", does not mean that its a problem).

  6. #6
    Join Date
    Oct 2007
    Location
    Seven Hills, NSW
    Posts
    159

    Default

    I would ask about tie down.

  7. #7
    Join Date
    Sep 2004
    Location
    Strzelecki Ranges Victoria
    Posts
    395

    Default

    Memphis, I was possibly one of the 'wannabies who dont know there a*s from their face . . .'
    I'd be interested in knowing what your qualifications are in stating so emphatically that the construction is ok and canning this guy who obviously has a concern & is looking for advice.
    Can you provide the location of any building code documentation that says that the load bearing support for the beam is correct and that the tie down requirements are complied with.
    Peter Clarkson

    www.ausdesign.com.au

    This information is intended to provide general information only.
    It does not purport to be a comprehensive advice.

  8. #8
    Join Date
    Jun 2007
    Location
    Perth, WA
    Posts
    67

    Default

    The beam in mention has nothing to do with roof tiedowns

    I was a roofie in WA for 12 months at one stage of my life. and my comments where not aimed at you, more the general opinion that if it looks sus, it is sus.

  9. #9
    Join Date
    Sep 2004
    Location
    Strzelecki Ranges Victoria
    Posts
    395

    Default

    If the beam is supporting roof members there is a very big chance that tie downs would come into play.
    I find it really annoying that people post to a forum with a genuine concern and receive garbage and get put down.
    Besides the tie down issue are you really saying that a steel beam supported by 4 stacked bricks is common & good practice in W.A.
    As building professionals we're constantly on a learning curve but I can't handle that this is correct building practice but I'm open to convincing.
    Peter Clarkson

    www.ausdesign.com.au

    This information is intended to provide general information only.
    It does not purport to be a comprehensive advice.

  10. #10
    Join Date
    Feb 2003
    Location
    Garvoc VIC AUSTRALIA
    Posts
    3,208

    Default

    Quote Originally Posted by Arc View Post
    I've had an independent building inspector in who also told me it is ok (prior to the 'braces' as well).

    I had expected the building inspector to be shocked by it but he practically ignored it for other issues.
    Professional opinion from onsite inspection
    Regards, Bob Thomas

    www.wombatsawmill.com

  11. #11
    Join Date
    Mar 2008
    Location
    Perth
    Posts
    6

    Default

    A few, shall we say, interesting responses.

    Yes, I posted on another forum a few weeks ago and got mixed views there, coming across this forum recently I thought I might get some more experienced and knowledgeable responses given the forum and topics I browsed through.

    Anyway, I was hoping someone in the know here could provide something specific from the building codes to confirm or allay my concern. If not, so be it, I was asking, not demanding. Personally, I just don't want to be the poor sucker that has to have something bad happen to me or my family for the practices to be changed...

  12. #12
    Join Date
    May 2004
    Location
    Melbourne, Australia
    Posts
    0

    Default

    Quote Originally Posted by Arc View Post
    The builder has told me this is fine (prior to the 'braces' being added). I've had an independent building inspector in who also told me it is ok (prior to the 'braces' as well).
    It would be interesting to know just how many bricks they would accept as "fine". Would 10 bricks stacked on top of each other be considered "fine" too

    To get a better idea of the situation, how is the other end of the beam supported? Can the beam move laterally?

  13. #13
    Join Date
    Jun 2007
    Location
    Perth, WA
    Posts
    67

    Default

    Quote Originally Posted by Arc View Post
    A few, shall we say, interesting responses.

    Yes, I posted on another forum a few weeks ago and got mixed views there, coming across this forum recently I thought I might get some more experienced and knowledgeable responses given the forum and topics I browsed through.

    Anyway, I was hoping someone in the know here could provide something specific from the building codes to confirm or allay my concern. If not, so be it, I was asking, not demanding. Personally, I just don't want to be the poor sucker that has to have something bad happen to me or my family for the practices to be changed...
    I will PM you a copy of the building code for framed construction in WA tomorrow, I had to get a copy of it when I added my second story

    I dont think it mentions a acceptable number of bricks though..

    But if possible, can you get a photo of anything else attached to the beam? All we know is its supporting air...

  14. #14
    Join Date
    Mar 2008
    Location
    Perth
    Posts
    6

    Default

    That would be great Memphis, thank you. I think the attached crude drawing I've knocked up illustrates things reasonably well (from what I can recall) - prior to the additional diagonal bracing. I don't think I have a photo that clearly shows the whole setup. Btw, the ceiling has just gone in so maybe it will be out of sight, out of mind now...

    I've had other people tell me of similar things in their own homes here in WA so I'm not expecting anything to be changed now, but I'd still like to know more about what is considered proper and professional building practices. There was an article I think linked from this forum about gutters not being made to Australian Standards, yet the majority of homes since the early 90's are using these gutters. Just because it's considered normal practice does not make it right.

  15. #15
    Join Date
    Feb 2008
    Location
    Aust
    Posts
    192

    Default

    The steel is a universal beam or UB. It is standard practice to do this and they are solids which is normal.
    Its been done for years. The carpenter has since checked props off the side.
    I take it there will probably be hangers checked into the side.
    Toms or props will be propped off the top off that.
    There is literally thousands of houses done in this manner.
    The brick wall will be 90mm. This is also standard for which the UB sits on. I would only be slightly concerned if the UB sat "right" on the corner of a 90mm wall.
    The roof is colour bond so there isn't a hell of a lot of weight.
    If the inspector was concerned he would say something.

    Do you have any images of timber that actually sits towards the middle rather than the ends of the beam? Toms? Under purlins? LVLs?

    It looks like a bulkhead or coffit ceiling? Whats its purpose?
    c2=a2+b2;
    When buildings made with lime are subjected to small movements thay are more likely to develop many fine cracks than the individual large cracks which occur in stiffer cement-bound buildings. Water penetration can dissolve the 'free' lime and transport it. As the water evaporates, this lime is deposited and begins to heal the cracks. This process is called autogenous healing.

Similar Threads

  1. pergola roof over tile house roof
    By Lbudgie in forum PERGOAS, GAZEBOS, STROMBELLAS & ROTUNDAS
    Replies: 3
    Last Post: 24th March 2006, 05:58 PM

Tags for this Thread

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •