    Quote Originally Posted by Sumodog View Post
    Integrity of insulation is stressed by applying DC current at 500 V (not double the supply voltage).
    I might pull my TAFE books out here. Perhaps the method has changed over the last few years.

  2. #17
    Join Date
    Sep 2007
    Location
    Thailand
    Age
    63
    Posts
    90

    Default

    I have to agree with you Timmo.

    Virtually all extension leads etc are rated at 0.6 to 1kV, therefore the correct test voltage should be 500 volts. This goes for V75/V105 PVC Building Wire as well.