29th June 2007, 08:27 PM #16
The drier you have is just a filter drier, not a burnout drier. The Alco driers are pretty much the best performing ones around. I work for the company that owns Alco controls and Copeland compressors so I have a pretty good understanding of the products, although i didnt realise the old Yorks ran them.
Depending on the size of the leak, the compressor would have been running low for some time which would cook the gas and oil breaking it down reducing its lubricity leading to the siezure. Losing a single charge of gas would not carry away enough oil to make it run dry.
It's possible its not acid contaminated but I'd personally test it myself to be sure.
The replacement of the outdoor unit sounds good. if the indoor unit works fine then flushing the pipework and pressure testing it sounds like a good way to go.
-
31st July 2007, 01:25 PM #17
It turns out that York can't supply a replacement outdoor unit for my AC system as it is too old. So I got the compressor replaced.
Didn't get the thermostat replaced. I was thinking of doing that for aesthetics but the AC guy said the old thermostats with the mercury switches are extremely reliable and probably better than a new one. Plus I was feeling cheap at the time.
The AC unit is outside our bathroom window so we could hear the AC guy swearing etc. Went out to see how he was going and he says yes its going fine. Come back inside and he resumes swearing.
He insisted it wasn't acid contaminated and didn't need a burnout drier as it didn't burn out. He reckoned it didn't smell like acid and the vac would clean any contamination out.
It's been a week now, and last night the outdoor unit wouldn't run after about 10pm (it was not that cold that it would shut off and anyway it didn't go onto emergency heat). This morning it is working again. Hope that's a one off.