    The sparky rocked up this morning and looked over everything. When he fitted the new 3 phase main switch, he placed 2 active wires for the shed main switch into the same active connector. Thus I only had 2 active phases in the shed.:
    Are you happy about that? Seems to me, any sparky I've every known, would have had his gonads grow back in, if he didn't know where a phase was going too.

  2. #17
    Join Date
    Jun 2004
    Location
    Grafton, N.S.W.
    Age
    63
    Posts
    1,142

    Default

    Yeah. It was no charge for yesterday fixing his error. And they are going to re-imburse me for the $92 it cost for the air con bloke to come out and "fix" the problem of the compressor running backwards too...
    Hooroo.
    Regards, Trevor
    Grafton

  3. #18
    Join Date
    Jul 2006
    Location
    Adelaide
    Posts
    2,661

    Default

    Quote Originally Posted by glock40sw View Post
    Well. Mystery solved.
    The sparky rocked up this morning and looked over everything. When he fitted the new 3 phase main switch, he placed 2 active wires for the shed main switch into the same active connector. Thus I only had 2 active phases in the shed. but when you placed a test light across the 3 actives in the shed it showed that they had power. but when the test light was put from active 1 to active 2 there was no light.
    So now the lathe is operational again and turned up a few nylon spacers today.
    Life is good with 3 phase.....
    as I said above...if you had measured between phases and not to earth it would have been revealed that something was amiss
    only 2 phases eg red to yellow and blue to red would have read 415V

    blue to yellow would have been 0 V...but reading all phases to an earth contact would have shown 240V on the meter

Similar Threads

  1. Electrical problem, but not many details.....
    By Reno RSS Feed in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 0
    Last Post: 5th July 2009, 12:30 AM
  2. Electrical - What Can The Problem Be?
    By Reno RSS Feed in forum PLUMBING
    Replies: 0
    Last Post: 7th March 2009, 11:10 PM
  3. Do I have a problem? (Electrical)
    By Dean in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 17
    Last Post: 23rd June 2004, 09:51 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •