    Default plate joining bearers mid span

    Hello All
    Can anyone tell me if joining bearers mid span between stumps with two 5mm steel plates and 4 m10 bolts is considered sound building practice?? Only the halved end is rotten and Id prefer not to be removing the 1800 of sound dry wood back to the next stump.
    Thanks for any advice.

  2. #2
    Join Date
    Aug 2003
    Location
    Pambula
    Age
    59
    Posts
    5,026

    Default

    Sounds dodgey to me but I'm not sure of the regs. I have a feeling that joins should only occur on top of a pier.

    Can't you run a steel C section from one stump to the next and bolt to the original bearer?
    "I don't practice what I preach because I'm not the kind of person I'm preaching to."

  3. #3
    Join Date
    Mar 2004
    Posts
    225

    Default

    Quote Originally Posted by capedcrusader
    Hello All
    Can anyone tell me if joining bearers mid span between stumps with two 5mm steel plates and 4 m10 bolts is considered sound building practice?? Only the halved end is rotten and Id prefer not to be removing the 1800 of sound dry wood back to the next stump.
    Thanks for any advice.
    In a word NO
    Its a definate no-no.

    Hooroo...
    I wanted to become a brickie but my old man said "No son, learn a trade."

  4. #4
    Join Date
    Apr 2004
    Location
    maybe next door
    Posts
    55

    Default

    Silent C
    I need a halving joint on the end to join to the side bearer - they built these houses so that the bottom plates of the side walls are bearer sized and at bearer level with the studs continuing down to these.
    [QUOTE=duckman]In a word NO
    Its a definate no-no.QUOTE]

    Duckman
    Could you tell me why maybe. Ive heard you can plate joint joists like this.

  5. #5
    Join Date
    Nov 2002
    Location
    Baffle Creek, QLD
    Age
    52
    Posts
    1

    Default

    The Timber Framing Manual only allows bearers to be joined over stumps.
    AS-1684.4
    Building Practice: Bearers 4.2.1.1

    Joints in bearers shall occur only over supports, with adequate bearing for both members ... All cuts shall be located over the support.
    ...
    The minimum bearing each side of the joint shall be 50 mm
    I'm not sure I understand your sitiuation though. Out of curiosity, how old is the house?

  6. #6
    Join Date
    Apr 2004
    Location
    maybe next door
    Posts
    55

    Default

    Hello Dylan SJ
    Im repairing the halving joint between the side wall and the rear wall bearers. The house is is about 100 years old.