    Default Vulcan Powerhouse 80- need help with fault on startup

    G'day fellas, just a query on my Vulcan branded, Powerhouse 80 model central heating unit. I went to switch it on, following all the standard instructions, and it will not ignite or start the heating sequence. The fault code directory on the panel points toward a fault that it calls : fault 3 (green led flashes 3 times then red led flashes for 10 seconds & repeats pattern continuously) "combustion air pressure system failure" is the description on the panel for this fault.

    My question is, can I reset or check anything before having to call out a service agent?
    It's frustrating, as we've just moved in after having tenants in here for 11 months, now we're finding all these "little" problems

    Any help would be appreciated!

    Cheers, Mike

  2. #2
    Join Date
    Sep 2007
    Location
    Thailand
    Age
    63
    Posts
    90

    Default

    The only info I could find that vaguely resembles your system is at the below link;

    http://www.ilecheating.com.au/entry_...try_frames.asp

    then click on "Comfort Control Remote Thermostat - Powerhouse" to download a manual, which may be of some use. Check the last page for info.

    If I was in your shoes, I'd try reseting it.
    “I do not think there is any thrill that can go through the human heart like that felt by the inventor as he sees some creation of the brain unfolding to success... Such emotions make a man forget food, sleep, friends, love, everything.” - Nikola Tesla.

  3. #3
    Join Date
    Mar 2008
    Location
    Eastern suburbs, Vic
    Posts
    5

    Default

    Thanks for the links & advice, been to that website before I jumped on here though. There's a reset button on the circuit board, which I've tried and also tried holding it down for 5 secs just to see if it would change anything- but to no avail... Also tried the reset button on the wall touchpad with the same result.

    I'm picking that there's a dodgy connection or even that something's blocked, given that the error signal reads as "combustion air pressure system failure" on the diagnosis panel. Is there something I can do or do a basic test on??

    Mike

  4. #4
    Join Date
    Sep 2007
    Location
    Thailand
    Age
    63
    Posts
    90

    Default

    Quote Originally Posted by Mixmaster View Post
    Thanks for the links & advice, been to that website before I jumped on here though. There's a reset button on the circuit board, which I've tried and also tried holding it down for 5 secs just to see if it would change anything- but to no avail... Also tried the reset button on the wall touchpad with the same result.

    I'm picking that there's a dodgy connection or even that something's blocked, given that the error signal reads as "combustion air pressure system failure" on the diagnosis panel. Is there something I can do or do a basic test on??

    Mike
    The only other thing you could try is to disconnect the unit from its' power supply (circuit breaker) & leave it off for 10 minutes then turn it back on.
    “I do not think there is any thrill that can go through the human heart like that felt by the inventor as he sees some creation of the brain unfolding to success... Such emotions make a man forget food, sleep, friends, love, everything.” - Nikola Tesla.

  5. #5
    Join Date
    Mar 2008
    Location
    Eastern suburbs, Vic
    Posts
    5

    Default

    Thanks for the advice, I'll try it tomorrow when the missus is off the computer

  6. #6
    Join Date
    Mar 2008
    Location
    Eastern suburbs, Vic
    Posts
    5

    Default

    Still no joy, turned the power off at mains and pulled batteries out of the wall touchpad as suggested. After doing all that, the fan still comes on, I cant hear any ignition spark sequence- as it has no manual ignition (fully automated by the looks ). Bloody thing... agghhh!

    Father in law to be may have a look at it this w/e, he's fairly switched on with these things.

    Any other suggestions guys?

    Mike

  7. #7
    Join Date
    Jun 2006
    Location
    the 'burn
    Posts
    118

    Default

    if a fault code is present and doesn't go away when you reset it, it's a very strong indicator that the fault is still there.

    read the manual in its entirety to try find the phrase "combustion air pressure system" and try find the physical location of it. It may be something as simple as a loose connection or a blockage, or it may warrant a service call.

    if it's still under warranty, don't try fix anything yourself, as the unit will no longer be under warranty.

    remember, the longer you delay in making the call, the longer it will take until the unit is fixed.

  8. #8
    Join Date
    Sep 2005
    Location
    Bendigo
    Age
    60
    Posts
    226

    Default

    The installation instructions for this model contain a small section on the function of the unit on startup:
    "When the comfort control calls for heat, the combustion fan commences operation. When air pressure at the burner reaches required level the pressure switch closes. A purge time of ten seconds elapses, then power is switched to the hot surface igniter."

    There is little other information in the instructions and it does not contain a physical diagram.

    If you are confident to look for yourself I would open the access panel and find out if the combustion fan is starting up and the pressure switch is not closing (blocked tube, faulty switch etc) or if the combustion fan is not starting up at all (faulty motor or relay etc).
    From previous statement it sounds like the combustion fan is starting up and I would be looking for a perished or loose tube running to the pressure switch or possibly a faulty switch.

    If not confident I would be calling a service agent.

    Dave.

  9. #9
    Join Date
    Apr 2008
    Location
    central vic
    Posts
    1

    Default Vulcan Powerhouse 80 LPG

    Hi Guys,
    I have a powerhouse 80 as well and have fault 7, (Ignition Failure)
    Cant really find any data on these units not even from Vulcan.
    I did do some investigating and found that the pressure sensing line into the combustion chaimber was not sealed correctly and would have been leaking combustion pressure, I have sealed that now and will test unit again soon,
    wondering if anyone has had simmilar problems??

  10. #10
    Join Date
    Jan 2007
    Location
    Adelaide - West
    Age
    43
    Posts
    311

    Default

    Combustion pressure fault, usually means the fan is not working, some times they just need a clean because they get rather heavy when covered in dust and wont spin. Could also be a blockage of dust from fan to heater, try a vacum in there.

    Ignition failures are usually one of three things
    1. The hot surface igniter has burnt out
    2. the flame failure saftey mechanism has burnt out
    3. the unit has overheated and blown a single use overtemperature cutout switch ( much like a fuse)
    IMHO these things should only be serviced by a good service agent, if they malfunction and don't work correctly the consequences can be deadly, including filling your house up with carbon monoxide as you sleep, or starting a fire within your wall cavity.
    If you dont play it, it's not an instrument!

  11. #11
    Join Date
    Jul 2004
    Location
    Sale
    Age
    69
    Posts
    559

    Default

    I'd be getting out a gas bloke to give it a clean and service. It's probably due for one anyway and if you stuff it up fiddling you will only cost yourself more in the long run. I've got an early Vulcan C80, without the fancy thermostat and if the unit is similar they tend to be cheapish to repair until they pack it in for good. Ours is 25 years old and still going strong.

  12. #12
    Join Date
    Mar 2008
    Location
    Eastern suburbs, Vic
    Posts
    5

    Default

    G'day Fella's, thanks for all the advice, haven't been back on here for a lil' bit...
    We have had it fixed by a knowledgeable heating & cooling bloke from the local paper. He said it had blocked suction tubes, no 240V supply through the pressure switch, dirty contacts on the main printed circuit board & the pressure switch was sticky. He's cleaned all the dirty bits and removed the blockage from the suction tubes. All for $140.00

    Just a tad different from the first bloke that came to the house, unfortunately when I wasn't here, and 'inspected' the unit to later tell me it was stuffed and would cost more to repair than to fix- pffft! Was going to replace it with a less than mid-efficiency Brivis unit for $1600 less the initial $100 "inspection/call out" fee. I'm sure glad I sourced a second opinion to say the least

    All said and done, we know there's a little hole in the heat exchanger, however, that's covered as the repair bloke's got a spare powerhouse 80, minus the main board, that we can buy off him for a song.

    Much better, quicker and safer to get a professional out- at least it's fixed properly now.

    Thanks again guys, Mike

Similar Threads

  1. vulcan powerhouse central heating - cutting out
    By msman in forum HEATING & COOLING
    Replies: 10
    Last Post: 4th July 2007, 10:47 AM
  2. Vulcan Heaters.
    By Vip in forum HEATING & COOLING
    Replies: 2
    Last Post: 26th August 2006, 05:57 PM

Tags for this Thread

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •