8th March 2008, 06:35 PM #16Novice
- Join Date
- Feb 2008
- Location
- Melbourne
- Posts
- 12
Answer! All the GPOs were wired in one circuit. Someone had tried to take the fridge GPO out of the loop by installing new wire from s/b to the second outlet. Unfortunately they didn't remove the original wire. Had it fixed and now fridge is on own circuit not on the rcd protected circuits.
Havent had a power outage yet so dont know if it has fixed the rcd trip.
-
8th March 2008, 07:59 PM #17
-
8th March 2008, 08:20 PM #18Senior Member
- Join Date
- Jan 2008
- Location
- Australia
- Posts
- 18
-
8th March 2008, 08:53 PM #19
-
8th March 2008, 09:20 PM #20
Options?
Could it be Hard wired in its own Circuit; and not go through a GPO?
I am thinking something like a Double Light Switch,
and remove one of the Switches,
replace it with a 20mm Nylon Alco Gland,
Wire into the Switch and all else you'd require is a Double BP for the earth.Navvi
-
8th March 2008, 09:48 PM #21
-
8th March 2008, 10:13 PM #22
No RCD
No Test and Tag......@ WorkNavvi
-
8th March 2008, 10:17 PM #23
-
10th March 2008, 12:51 PM #24Member
- Join Date
- May 2006
- Location
- Perth
- Posts
- 71
What about aircons? my aircon was installed not going into the RCD.
-
10th March 2008, 01:34 PM #25Senior Member
- Join Date
- Jun 2006
- Location
- the 'burn
- Posts
- 118
-
10th March 2008, 02:56 PM #26Member
- Join Date
- Oct 2006
- Location
- Brisbane
- Posts
- 59
good luck
This sound like a typical electrical install, they don't give a toss till they get caught, worst thing about this is you get a new electrician round, he will say this needs doing, that needs doing it's going cost xxxx you can't get out of paying him to do the work and he's probably just as bad as the last bloke, sometimes worst !!!! which is really bloody great. you say anything about their quality of work and that gets there back up!!!!Hope you get it sorted to your satification with out to much inconvenience to yourself. With the trip switches I have seen/used some machinery with this type of switch not for domestic application though.