problems with split system install
guy's.just had a panasonic 8.1 kw reverse a/c installed the pipe run was 10m (ish) we had a funny noise when we turn the unit on and after a few days the system started to not cool as desired, so I got the bloke back that had installed the unit he checked a few things then sprayed some stuff in which he said would stop a leak. (as this reacts with the air).Also said the there was still positive pressure in the unit so no air had got in. After this he then put some more 410 gas in to the correct pressure and said all was well, this happened last night the unit was working well last night for the time we had it on.The question I have is does anyone use this stuff that he sprayed in ??how safe is it to use ??what are the long term affects on the unit I have ???was this just a quick fix/she'll be right mate solution.The stuff was in a blue tin and was a throw away after the one charge (did not manage to catch the name and woogle has drawn a blank which is a worry.Any information would be appreciated.Davo
-
8th February 2008, 04:06 PM #2Member
- Join Date
- Dec 2006
- Location
- Canberra
- Age
- 45
- Posts
- 93
i've seen the stuff at Actrol but I only fix leaks the old fashioned way. You should really only use it when you really can't find the leak. Even though they claim it to be compatible, it still contaminates the oil.
Im concerned that is was to a new unit. Even though R410a is a near zeotropic blend, it's still a blend. He really should have recovered, leak tested with nitro, repaired and evacuated before setting it back to work.
-
9th February 2008, 05:24 AM #3Banned
- Join Date
- Jul 2007
- Location
- Melbourne
- Posts
- 105
-
9th February 2008, 06:18 PM #4Intermediate Member
- Join Date
- Feb 2007
- Location
- south australia
- Posts
- 0
hello i have been in the trade for over 13 years never used the stuff and never will. as stated r410a is a blend, any loss of gas in a 400 range of gas is a blend and needs to be removed after a leak and discarded. as stated the system needed to be pressure tested with nitrogen at around 2000KPA for 24hours.. then properly evacuated and charged with new R410a. i would start to wonder after his current behaviour if he has even used the correct pipe and carried out the work properly..
-
9th February 2008, 08:56 PM #5Senior Member
- Join Date
- Jan 2008
- Location
- Australia
- Posts
- 18
-
10th February 2008, 12:06 AM #6Member
- Join Date
- Dec 2006
- Location
- Canberra
- Age
- 45
- Posts
- 93
It's not spray on, it's a dump in goop that is pushed into the system, much like the "no more leaks" for tyres.
It dries as it's pushed out of the pipework.
-
10th February 2008, 02:46 PM #7New Member
- Join Date
- Feb 2008
- Location
- sydney
- Posts
- 1
I agree - have only ever used this nasty stuff once in a friends car - worked for a few days and compressor seized....
I have been installing splits for many years now and find it difficult to believe that a tradie can be so bone idle lazy as to not trace a leak on a simple split.... it's not rocket science people...
What worries me is that the "installer" has used this in a brand new unit. This will surely void any future warranty claims if and when (actually definitely WHEN) the compressor fails?
-
10th February 2008, 03:50 PM #8Senior Member
- Join Date
- Jan 2008
- Location
- Australia
- Posts
- 18
-
11th February 2008, 10:51 AM #9Member
- Join Date
- Oct 2006
- Location
- Brisbane
- Posts
- 59
thanks for all the response
guys
Thanks for all your replys will try to get the bloke back round and discuss what we can do to rectify this situation, i really would like him to purge the pipes and correct the leak then refill with gas. (which is what he should do as we are see signs of poor cooling againg.(i will let you know how I go). one of those situations that you dread.
cheers anyway even if it did start to go off topic !!!
-
11th February 2008, 02:02 PM #10
Have moved everything to the Help-Mouse ate my fujitsu split system head aircon electronics thread, as this is davo_scuba's thread and it is not fair for him to have wade through the whole thread to find what is relevant to his problem.
DJ
Super Moderator
Woodworking Australia's
WOODWORK FORUMS
-
11th February 2008, 09:01 PM #11Member
- Join Date
- Jun 2007
- Location
- Tasmania
- Posts
- 8
I totally agree. There are four connections that he had to leak test/re-flare or tighten flare if leaking. If he didn't find a leak on one of his four connections, then it's a warranty problem and Panasonic should repair/replace the unit.
I've never seen the stuff, but it's a few years since I was doing refirigeration work, but I would be rather concerned about this sort of thing being put into a split system. I replaced several reversing valves in heat pumps, the crap surely wouldn't do them any good, let alone the capillaries and the compressor. I'd highly doubt that manufacturers would honour any warranties with any sort of "stop leak" goop.
Though it does sound like it would be handy for that last ditch attempt at keeping something running for another month or two!
-
11th February 2008, 09:08 PM #12Senior Member
- Join Date
- Jan 2008
- Location
- Australia
- Posts
- 18
-
11th February 2008, 10:16 PM #13Member
- Join Date
- Jun 2007
- Location
- Tasmania
- Posts
- 8
-
12th February 2008, 12:08 AM #14Novice
- Join Date
- Jan 2006
- Location
- Glen Waverly
- Age
- 47
- Posts
- 17
I'd guess that it would have been one of the super seal products, personally I have no experience with them.
you can find more info here on the applications/specs.
http://www.cliplight.com/hvacr/products.php?catID=27
-
13th February 2008, 05:07 PM #15Member
- Join Date
- Dec 2006
- Location
- Canberra
- Age
- 45
- Posts
- 93
Similar Threads
-
What is a good split system?
By goraek in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etcReplies: 17Last Post: 6th January 2008, 04:12 PM -
split system cables
By zelig in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etcReplies: 4Last Post: 5th November 2007, 09:45 PM -
Relocate split system
By jimc in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etcReplies: 5Last Post: 21st February 2007, 04:54 PM -
3 phase split system
By tcns in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etcReplies: 3Last Post: 21st December 2006, 12:03 AM -
Reducing cost of split system Air Con install
By Wildman in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etcReplies: 25Last Post: 10th October 2006, 08:02 PM
Bookmarks