Gas Pipe Sizing
Hi there all
I am new to posting but have been watching and absorbing for a number of years.
Have a question. We are getting a gas log fire installed and the guy there said 1/2" copper pipe for the gas feed would be OK so I have got myself a 18m roll of said stuff.
I want to run the pipe in from point A to point B ready for the Logfire installer to hopefully save on labour (I don't mind the grovelling under the house).
To cut a long story short can anyone tell me if 1/2" pipe over a length of 15m will be OK for the logfire (which is rated at 32MJ/hr). It will connect to a 3/4 Galv Gas pipe main. Also on this branch feeds the Gas cooktop (up to 39MJ/hr).
Again, I am not connecting just supplying the pipe and labour under the house. I probably should have got the plumber out first before purchasing the pipe. But anyway if anyone can tell me some gas pipe sizing info that would be good
Steve
-
25th October 2007, 06:36 PM #2SENIOR MEMBER
- Join Date
- Aug 2005
- Location
- Victoria
- Posts
- 412
Did you get the right grade of pipe?
Tools
-
25th October 2007, 07:15 PM #3
I'd need to know the inlet pressure and the connection size of the heater.
Doesn't sound like it's ok tho.If you dont play it, it's not an instrument!
-
25th October 2007, 10:23 PM #4Senior Member
- Join Date
- Jul 2007
- Location
- Sydney-south
- Posts
- 333
Regulated pressure, mj ratings, length of run from meter. Correct grade pipe? I cant remember exactly, Ill have to look it up but 1/2" pipe has a limitation on how far it can be run its 3 or 5 metres, and probably wouldnt support the amount of gas a 'log fire' needs. A run of 15m may increase the index length of the installation and the MJ rating of a decorative log fire will significantly increase the MJ rating of the installation and may require the WHOLE installation be resized, not to mention the meter and regulator.
Plumbers were around long before Jesus was a carpenter
-
26th October 2007, 08:48 AM #5New Member
- Join Date
- Mar 2004
- Location
- Melbourne
- Age
- 62
- Posts
- 5
The pipe I got was 0.91mm. The heater has a 1/2" (15mm) connection.
The 3/4 Galv that would feed this comes off the bigger main (also galv) which looks like about 1.5".
Originally there was an old Vulcan Wall Furnace running off the same distance 1/2" copper so I figured this new one would be OK.
Anyway I have the plumber who is doing the actual connections coming tommorrow morning to have a look and talking to him on the phone he thinks 3/4 copper will be the go. Luckily I can swap the pipe and pay the difference.
Maybe shouldn't just rely on what the Gas logfire guy says and actually talk to those in the know (ie this forum first - it is free)
-
27th October 2007, 06:10 PM #6Novice
- Join Date
- Sep 2006
- Location
- sydney
- Posts
- 23
You can do the last 6-8 metres in 1/2" for 32-38mj/hr guessing the rest of the details based on where you live. If you were in Sydney I might say to get a 2.75kpa regulator at the meter then you could do that run in 1/2".
-
28th October 2007, 12:08 PM #7
-
28th October 2007, 06:09 PM #8Senior Member
- Join Date
- Jul 2007
- Location
- Sydney-south
- Posts
- 333
Plumbers were around long before Jesus was a carpenter
-
29th October 2007, 07:52 AM #9New Member
- Join Date
- Mar 2004
- Location
- Melbourne
- Age
- 62
- Posts
- 5
Thanks for feedback all.
My Plumber came on Saturday and he said 3/4 was the way to go so luckily I was able to return the 1/2" and upgrade.
The Plumber seemed quite happy for me to grovel under the house and run the pipe in and he will do the connections. The price he gave me (seemed quite low to me) may have reflected this.
-
29th October 2007, 04:07 PM #10Senior Member
- Join Date
- Jul 2007
- Location
- Sydney-south
- Posts
- 333
Glad you got it sorted mate, it is a bonus if someone is willing to crawl around on their guts under a house for you.
Plumbers were around long before Jesus was a carpenter
Similar Threads
-
Broken Pipe inside Pool shell
By PhilMcCrackin in forum POOLS, SPA & WATER FEATURESReplies: 2Last Post: 30th October 2007, 02:26 PM -
Silver soldering 3/4 inch pipe with MAPP gas
By emptybucketman in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etcReplies: 7Last Post: 6th July 2007, 10:56 PM -
Gas hot water heaters
By Bob Willson in forum NOTHING AT ALL TO DO WITH RENOVATIONReplies: 28Last Post: 29th March 2005, 12:16 PM -
Australian Goverment Pipe Specifications
By trevorZ in forum JOKESReplies: 1Last Post: 28th May 2003, 12:59 AM
Bookmarks