    Hi All,
    I'm looking for advice/information on the best way to bury a stormwater pipe.

    The pipe will be going under our driveway (gravel) and will probably be no less that 1 foot below the surface. The pipe will be going to a water tank.

    We only get light vehicles on the driveway (cars and possibly a 4WD - no large trucks, etc)

    What size/class pipe should I use - will normal 90mm be OK?
    Should I encase the pipe in concrete - or should I just surround it in sand and then backfill?

    Any and all advice appreciated.
    Cheers.

    Vernon.
    __________________________________________________
    Bite off more than you can chew and then chew like crazy.

  2. #2
    Join Date
    Nov 2005
    Location
    Kilsyth
    Age
    66
    Posts
    300

    Default

    Quote Originally Posted by Vernonv View Post
    Hi All,
    I'm looking for advice/information on the best way to bury a stormwater pipe.

    The pipe will be going under our driveway (gravel) and will probably be no less that 1 foot below the surface. The pipe will be going to a water tank.

    We only get light vehicles on the driveway (cars and possibly a 4WD - no large trucks, etc)

    What size/class pipe should I use - will normal 90mm be OK?
    Should I encase the pipe in concrete - or should I just surround it in sand and then backfill?

    Any and all advice appreciated.
    90mm stormwater pipe is fine, but I would be going deeper than 300mm (actually, I did go deeper, 900mm, but I have a mate who has a small back hoe, here he is trying to knock down my garage (please note, custom built garage ) [ame="http://www.youtube.com/watch?v=ejAxk9PX96I"]LINK[/ame]


    anyways, I would not go less than about 500mm depth for pipe that is likely to have vehicle traffic, other option would be to dig the trench 400mm deep, 350mm wide and lay 270mm concret pipe, and slide your 90mm stormwater through that, then just backfill the trench with sand, and top over with crushed rock.

  3. #3
    Join Date
    Oct 2003
    Location
    Kentucky NSW near Tamworth, Australia
    Age
    86
    Posts
    1,067

    Default

    I think 300mm to the top of the pipe will be fine provided the trench is kept to just clearance at the sides of the pipe because there wouldn't be much pressure on the top of the pipe. I have seen storm water pipe at less depths without any problems.

  4. #4
    Join Date
    Oct 2006
    Location
    Armidale NSW
    Age
    53
    Posts
    299

    Default

    Thanks Guys.

    So Barry, what your are suggesting is to only have the trench wide enough to fit the pipe?

    Should I surround the pipe with sand (or similar material) before backfilling or doesn't it matter?

    Terrain - my shed it coming along nicely - will be good having 7.5 x 12 of workshop space and another 3 x 12 covered area for storage (awning off shed). I should post some pics up.
    Cheers.

    Vernon.
    __________________________________________________
    Bite off more than you can chew and then chew like crazy.

  5. #5
    Join Date
    Nov 2005
    Location
    Kilsyth
    Age
    66
    Posts
    300

    Default

    Quote Originally Posted by Vernonv View Post
    Thanks Guys.

    So Barry, what your are suggesting is to only have the trench wide enough to fit the pipe?

    Should I surround the pipe with sand (or similar material) before backfilling or doesn't it matter?
    What Barry says is true, to a point, if the ground is very stable, ie: bloody near rock hard to dig, 1/4 minus (7mm) stone around the pipe.

    Terrain - my shed it coming along nicely - will be good having 7.5 x 12 of workshop space and another 3 x 12 covered area for storage (awning off shed). I should post some pics up.
    7m wide x 6m deep is my garage, 6m x 6m shed going in behind it (at some stage

  6. #6
    Join Date
    Jan 2002
    Location
    Melbourne, Aus.
    Age
    71
    Posts
    0

    Default

    Wouldn't hurt if you had some gravel or scoria to lay it in and to put over it. That's a requirement where I am with PVC sewer pipes even if they're 3m down.
    Cheers, Ern

  7. #7
    Join Date
    Jan 2007
    Location
    Adelaide - West
    Age
    43
    Posts
    311

    Default

    I normally use 100mm sewer grade pipe, it's stronger and much more suited to rodding if it ever gets blocked.
    If you dont play it, it's not an instrument!

  8. #8
    Join Date
    Oct 2003
    Location
    Kentucky NSW near Tamworth, Australia
    Age
    86
    Posts
    1,067

    Default

    Quote Originally Posted by Vernonv View Post
    Thanks Guys.

    So Barry, what your are suggesting is to only have the trench wide enough to fit the pipe?

    Should I surround the pipe with sand (or similar material) before backfilling or doesn't it matter?

    Terrain - my shed it coming along nicely - will be good having 7.5 x 12 of workshop space and another 3 x 12 covered area for storage (awning off shed). I should post some pics up.
    I have stormwater pipes that are only about 2 inches under the ground that are in Granite sand that have been there for 20 years that I have driven my ride on mower as well as my Toyota Hilux over with out any damage so I would suggest using some sand around the sides and an inch on the top and refill with the natural soil dug out of the trench but dig the trench with very little clearance around the pipe.

  9. #9
    Join Date
    Dec 2005
    Location
    Gold Coast
    Age
    67
    Posts
    239

    Default

    I'd basically go just a little deeper (two foot) or put a bit of concrete over the top of it where it goes under the driveway. This is simply because, after heavy rain (remember it?) when the ground is waterlogged, a heavy vehicle can sometimes have a wheel sink down and crush them. This happend to me when my brother drove his Land Cruiser over mine.

    If you can keep them well below what a vehicle's wheel would reach in a bog, you should be OK.

  10. #10
    Join Date
    Oct 2006
    Location
    Armidale NSW
    Age
    53
    Posts
    299

    Default

    Thanks for the input everyone.

    Rossluck - the ground where the pipe is going is pretty well compacted and we have never had any issues with it getting boggy, etc.

    Thanks for clarifying that Barry - sounds like the way to go.

    Bricks (I was wondering when you were going to post) - can you get fittings to go from 90mm stormwater to 100mm sewer. Also I saw somewhere that there is a heavy duty version of the 90mm stormwater - would it be any good?
    Cheers.

    Vernon.
    __________________________________________________
    Bite off more than you can chew and then chew like crazy.

  11. #11
    Join Date
    Nov 2005
    Location
    Kilsyth
    Age
    66
    Posts
    300

    Default

    Quote Originally Posted by Vernonv View Post
    T
    Bricks (I was wondering when you were going to post) - can you get fittings to go from 90mm stormwater to 100mm sewer. Also I saw somewhere that there is a heavy duty version of the 90mm stormwater - would it be any good?
    pretty standard fitting, 100mm to 90mm adaptor, bunnings sell them , as would almost any place that has plumbing supplies (even your local garden supplies is likely to have them.

  12. #12
    Join Date
    Jan 2007
    Location
    Adelaide - West
    Age
    43
    Posts
    311

    Post To Vernov.

    You can buy fittings to go from 90mm stormwater to 100 mm pvc, conveniantly it called a 90mm stormwater to 100pvc adaptor, ( not taking the mate, that's what its called).

    For some reason you can get sqaure downpipe- 90 stormwater, but not to 100 pvc. But you can adapt after.

    The thicker stormwater pipe i've not had anything at all to do with, I'll be honest mate i'm a stubborn git at times, and not using stormwater grade pipe is one of my quirks. So as for if it's good? I cant honestly tell you.


    When you dig the trench make the trench 100 mm wider and deeper and fill with sand to 100 above the pipe. This will stop little rocks punching through the side of the pipe when you backfill. If when you dig the trench the dirt is reletively loose and fine, Not in clumps bigger than around 20mm of dirt and there arn't a noticeable amount of rocks, you could probably get a way with using the same stuff as backfill.

    To work out how much backfill you need-
    Length x width x height ( in meters.) x by 1.8 will give you the approximate tonnage of what you need to order.
    If you dont play it, it's not an instrument!

  13. #13
    Join Date
    Jul 2007
    Location
    Sydney-south
    Posts
    333

    Default

    The 100mm stormwater pipe, if you can find it seems to be ok as far as stormwater pipe goes, has a similar wall thickness to the 6" stuff. You dont see it much here in sydney but Im with Bricks as far as the 90mm rubbish goes, better off spending the extra and buying 4"sewer (DWV) pipe and fittings, it will save you in the long run.
    Plumbers were around long before Jesus was a carpenter

  14. #14
    Join Date
    Oct 2006
    Location
    Armidale NSW
    Age
    53
    Posts
    299

    Default

    Thanks for the additional info guys.

    Ok, so I'll go for the 100mm sewer and make sure that I surround the pipe in sand (thanks for the formula Bricks).
    Cheers.

    Vernon.
    __________________________________________________
    Bite off more than you can chew and then chew like crazy.

  15. #15
    Join Date
    Jan 2007
    Location
    Adelaide - West
    Age
    43
    Posts
    311

    Default

    You can change the down pipes to round Pvc Eg; 65mm for easy hook up to underground system too.
    If you dont play it, it's not an instrument!

Similar Threads

  1. New Stormwater pipe
    By ptwelves in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 11
    Last Post: 28th October 2006, 08:55 AM
  2. Howto:- Repair hole in stormwater pipe
    By ptyltd in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 9
    Last Post: 23rd July 2006, 04:58 PM
  3. ag pipe to stormwater
    By XT4V in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 3
    Last Post: 23rd April 2006, 12:52 PM
  4. Connecting Ag pipe to 90mm Stormwater
    By VegasDave in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 8
    Last Post: 8th May 2005, 08:54 PM
  5. Replies: 1
    Last Post: 28th May 2003, 12:59 AM

Tags for this Thread

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •