Thread: Gpo In Bathroom

  1. #1
    Join Date
    Feb 2007
    Location
    WA
    Posts
    45

    Default Gpo In Bathroom

    Just wondering if there is a minimum distance above a bathroom vanity required for a new power outlet. I currently have 100mm but need to drop it down due to buying a larger than thought mirror.
    Regards
    Greg

  2. #2
    Join Date
    Jan 2007
    Location
    Katoomba NSW
    Posts
    332

    Default

    Greg the GPO is not allowed within an area 400mm above and 150mm to the sides of the basin.
    Check with your electrician before attaching the mirror.
    Those were the droids I was looking for.
    https://autoblastgates.com.au

  3. #3
    Yonnee's Avatar
    Yonnee is offline Trailer Bloke & Mild Mannered Moderator
    Join Date
    May 2007
    Location
    Tooradin, Vic.
    Age
    52
    Posts
    484

    Default

    I was under the impression that it was 600mm from any water source??
    Too many projects, so little time, even less money!
    Are you a registered member? Why not? click here to register. It's free and only takes 37 seconds! Doing work around the home? Wander over to our sister site, Renovate Forum, for all your renovation queries.

  4. #4
    Join Date
    Jan 2007
    Location
    Katoomba NSW
    Posts
    332

    Default

    Quote Originally Posted by Yonnee View Post
    I was under the impression that it was 600mm from any water source??
    No.
    Sect 7.1 of AS3000. It depends on the volume of the water container.
    Those were the droids I was looking for.
    https://autoblastgates.com.au

  5. #5
    Join Date
    Jan 2005
    Location
    Newcastle/Tamworth
    Posts
    416

    Default

    NCarcher is spot on..

  6. #6
    Join Date
    Sep 2007
    Location
    Thailand
    Age
    63
    Posts
    90

    Default

    Quote Originally Posted by gregt View Post
    Just wondering if there is a minimum distance above a bathroom vanity required for a new power outlet. I currently have 100mm but need to drop it down due to buying a larger than thought mirror.
    Regards
    Greg
    As already suggested, this is not permitted unless other conditions have been met. Below is the AS/NZS 3000:2000 ruling. I have bolded the important parts. To further clarify, you wish to install a GPO in 'zone 2'.



    7.1.4.2 Socket-outlets.

    Socket-outlets shall not be installed within 0.3 m of the floor of a bathroom,laundry or other similar location where the floor is likely to become wet.

    In addition, and regardless of the degree of protection provided by the equipment, the following conditions shall apply to the installation of socketoutlets in the classified zones:

    (a) In Zones 0 and 1 socket-outlets shall not be permitted.
    (b) In Zone 2, socket-outlets shall not be permitted unless they—
    (i) have automatic switching and are incorporated in a shaver supply unit complying with AS/NZS 3194; or
    (ii) are protected by a RCD with a maximum rated residual current of 30 mA; and
    (iii) are enclosed in a cupboard provided that the enclosure is maintained during the normal operation of the connected equipment.

    In summary, the only way that you can install a GPO in the location that you wish, is to make sure that it is RCD protected AND it is enclosed in a cupboard provided that the enclosure is maintained during the normal operation of the connected equipment.
    “I do not think there is any thrill that can go through the human heart like that felt by the inventor as he sees some creation of the brain unfolding to success... Such emotions make a man forget food, sleep, friends, love, everything.” - Nikola Tesla.

  7. #7
    Join Date
    Feb 2007
    Location
    WA
    Posts
    45

    Default

    Is that right. I have two bathrooms in our new house and they both have power outlets above the vanity basin to the side. They are all RCD protected. Does this mean they are illegal? The electrician put them there!
    Greg

  8. #8
    Join Date
    Aug 2002
    Location
    Boyne Island, Queensland
    Age
    52
    Posts
    176

    Default

    How far to the side of the basin are they?
    Dan

  9. #9
    Join Date
    Aug 2007
    Location
    Yanderra nsw
    Posts
    28

    Default

    i am looking at the pic in AS:3000 right now and as said if the capacity is less than 45L it must be 400mm above or 150mm to the side(this is to the closest edge of the GPO.
    Hope that helps.

  10. #10
    Join Date
    Aug 2007
    Location
    Yanderra nsw
    Posts
    28

    Default

    My rules say they are not permitted in zone 0,1 or 2 at all only in zone 3 which is outside above measurements

  11. #11
    Join Date
    Aug 2002
    Location
    Boyne Island, Queensland
    Age
    52
    Posts
    176

    Default

    Quote Originally Posted by another termite View Post
    My rules say they are not permitted in zone 0,1 or 2 at all only in zone 3 which is outside above measurements
    It may help if you quote the clause and standard you're looking at so we can follow,
    Dan

  12. #12
    Join Date
    Feb 2007
    Location
    WA
    Posts
    45

    Default

    It is a 1200mm vanity so the power point would be approx 500mm to one side and up 100mm from the vanity top. I've seen it heaps of times before. There must be another clause. Maybe Santa can help.

  13. #13
    Join Date
    Sep 2007
    Location
    Thailand
    Age
    63
    Posts
    90

    Default

    As per AS/NZS 3000:2000, purchased 2006, with amendments 1,2 & 3, Fig 7.1C(a) & Table 7.1;

    I'll have to do this in 2 separate posts...file size too big.
    “I do not think there is any thrill that can go through the human heart like that felt by the inventor as he sees some creation of the brain unfolding to success... Such emotions make a man forget food, sleep, friends, love, everything.” - Nikola Tesla.

  14. #14
    Join Date
    Sep 2007
    Location
    Thailand
    Age
    63
    Posts
    90

    Default

    Here is the next pic...had to change to GIF.

    Also, this may help;

    7.1.2.2 Other fixed water containers.
    The requirements for fixed water containers other than baths and showers are based on the dimensions of the following two zones (examples are given in Figure 7.1C):
    (a) Zone 0 shall be the area of the interior of the water container.
    (b) Zone 2 shall be—
    (i) for individual water containers with a capacity not exceeding 45 L, the area limited by—
    (A) the vertical plane 0.15 m from the internal rim of the water
    container; and
    (B) the floor and the horizontal plane 0.4 m above the water
    container; and

    NOTE: Figure 7.1C(a) shows a typical double bowl sink where the capacity of each container does not exceed 45 L.
    (ii) for water containers with a capacity exceeding 45 L, the area limited by—
    (A) the vertical plane 0.5 m from the internal rim of the water
    container; and
    (B) the floor and the horizontal plane 1.0 m above the water
    container.
    NOTES:
    1 There are no Zones 1 or 3 associated with these water containers.
    2 The zones do not extend beyond the boundaries of the room.
    “I do not think there is any thrill that can go through the human heart like that felt by the inventor as he sees some creation of the brain unfolding to success... Such emotions make a man forget food, sleep, friends, love, everything.” - Nikola Tesla.

  15. #15
    Join Date
    Sep 2006
    Location
    Bermagui
    Age
    73
    Posts
    4

    Question Whatt??

    Uhuh, so now I really understand! Can I really have a powerpoint in the bathroom I am currently building or should I just run an extension lead out the door?

Similar Threads

  1. Bathroom Renovation Project
    By juan in forum BATHROOM & TOILET
    Replies: 152
    Last Post: 3rd May 2008, 04:58 PM
  2. Complete Bathroom in a Day
    By batcat in forum BATHROOM & TOILET
    Replies: 3
    Last Post: 31st January 2007, 12:41 PM
  3. How to most out of a Small bathroom?
    By Ayesha in forum KITCHENS, BATHROOMS, THEATRES, etc
    Replies: 13
    Last Post: 21st August 2006, 08:17 PM
  4. Installing GPO in cupboard
    By Trav in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 12
    Last Post: 16th January 2006, 04:53 PM

Tags for this Thread

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •