    Default sandwiching lvl for bearers

    hi all,
    I have a 6.6 x 360 x 45 piece of lvl that i intend to cut to make two 6.6 x 140 x 45 pieces that I will sandwich to make a bearer that is 6.6 x 140 x 90.

    My questions are:
    1. Can I use a circular saw with a guide to cut the beam?
    2. Is there any recommended way to sandwich the two pieces? Glue, nails, etc?
    3. with the two pieces sandwiched there will be a small groove on top and bottom of the combined beam as the corners of the wood are slightly rounded. Should this be shaved smooth? Will it trap water if I dont?
    4. Also what is the recommended way to insulate the floor whilst it is being built.
    Thanks
    Greg

  2. #2
    Join Date
    Aug 2003
    Location
    Pambula
    Age
    59
    Posts
    5,026

    Default

    Check page 4 and 5 of this document: http://www.chhfuturebuild.com/upload...bles_Mch06.pdf
    "I don't practice what I preach because I'm not the kind of person I'm preaching to."

  3. #3
    Join Date
    Mar 2004
    Location
    Carine WA
    Age
    75
    Posts
    110

    Default

    Quote Originally Posted by gg23 View Post
    hi all,
    I have a 6.6 x 360 x 45 piece of lvl that i intend to cut to make two 6.6 x 140 x 45 pieces that I will sandwich to make a bearer that is 6.6 x 140 x 90.
    Unless you NEED to have the beam this height, ie 140mm DON'T cut it, as it is MUCH stronger at 360mm high than two at 140mm.
    Kind Regards

    Peter

  4. #4
    Join Date
    Jul 2007
    Location
    reservoir
    Posts
    39

    Default

    Quote Originally Posted by silentC View Post
    Check page 4 and 5 of this document: http://www.chhfuturebuild.com/upload...bles_Mch06.pdf
    thank you. This is an excellent resource. Not sure what elastometric adhesive is, Aquadhere??

    Thanks again
    greg

  5. #5
    Join Date
    Jul 2007
    Location
    reservoir
    Posts
    39

    Default

    I have to have bearers of 140, and then joists of 90. Btw the engineers recommended joist of 95 x 45 F17, but I am unable to find this dimension. Can I use 90 x 45 F17?

    Thanks
    greg

  6. #6
    Join Date
    Aug 2003
    Location
    Pambula
    Age
    59
    Posts
    5,026

    Default

    You'd have to ask the engineers that. 95 seems an odd size for hardwood though - my span tables list either 100m or 90mm depending on the span/rating. My joists are 95mm but they're LVL.
    "I don't practice what I preach because I'm not the kind of person I'm preaching to."

  7. #7
    Join Date
    Jul 2007
    Location
    reservoir
    Posts
    39

    Default

    Hi,
    Will be using f17 for the joists even though the engineers specs ask for 95 x 45 LVL, as it is cheaper. Have cleared the substitution with the engineer. Just need to sort out the size. So i guess to be on the safe side, I should use 100 x 45 F17 for the joists. On another note Ive read somewhere that you can cut grooves in lvl bearers as long as they are not greater than 25mm (from memory). Is this really ok? Doesnt it weaken the bearer? I ask this as we have made an error with the stump heights and therefore our floor will sit about 3cm higher than originally planned.

    Thanks again for your help, this site is a godsend,
    greg

  8. #8
    Join Date
    Aug 2003
    Location
    Pambula
    Age
    59
    Posts
    5,026

    Default

    Again, I'd run that past the engineer - it is his backside on the line if it fails.

    Regarding the joists, if you tell me the span, I can look it up in the tables - they're NSW tables but based on Australian Standards so should be OK (I think Reservoir is in Vic.).
    "I don't practice what I preach because I'm not the kind of person I'm preaching to."

  9. #9
    Join Date
    Jul 2007
    Location
    reservoir
    Posts
    39

    Default

    hi silentC
    The joists span 3.8 metres, across 3 stumps. Maybe I'll leave the bearers alone.

    greg

  10. #10
    Join Date
    Aug 2003
    Location
    Pambula
    Age
    59
    Posts
    5,026

    Default

    What you need to tell me is the widest span that a joist has to cover between bearers. For example, if by the above you mean that you have three bearers evenly spaced at 1.9 metres, then the joist span is 1.9 metres: my table says that for up to 2.1 continuous span you can use 90x45 F17 seasoned timber joists at 450 or 600 centres. Continuous span means that the joist spans at least 3 bearers, which I gather it does in your case.
    "I don't practice what I preach because I'm not the kind of person I'm preaching to."

  11. #11
    Join Date
    Jul 2007
    Location
    reservoir
    Posts
    39

    Default

    hi silentC,
    The you are correct in that the joist span is 1.9m, but the plan from the engineer states that the joists must be continuous. I assume this means that the joists must be 3.8m. Does this change the info that you have given me? Also do you know what KD hardwood rated at?
    greg

  12. #12
    Join Date
    Aug 2003
    Location
    Pambula
    Age
    59
    Posts
    5,026

    Default

    the plan from the engineer states that the joists must be continuous. I assume this means that the joists must be 3.8m
    True. The sizes I gave you are from the table for continuous spans, so that's what you should use.

    do you know what KD hardwood rated at?
    It should be F17 but best to tell the timber yard that's what you want when you order.
    "I don't practice what I preach because I'm not the kind of person I'm preaching to."

  13. #13
    Join Date
    Jul 2007
    Location
    reservoir
    Posts
    39

    Default

    i am considering buying the KD Hardwood from a builder who is no longer intending on using it. He states that it is not stamped, but was purchased with the same intention, ie for joists.

    thanks again for your help,
    greg

  14. #14
    Join Date
    Aug 2003
    Location
    Pambula
    Age
    59
    Posts
    5,026

    Default

    I can't really give you any advice on what to do there. I'd probably speak to the engineer.
    "I don't practice what I preach because I'm not the kind of person I'm preaching to."

  15. #15
    Join Date
    Jul 2007
    Location
    reservoir
    Posts
    39

    Default

    spoke to the engineer. Said it was fine as long as it is f17 KD hardwood? In a bind as the price is great, the seller reckons it should be fine, but dont want any hassles with the inspector. What to do?

    greg

Similar Threads

  1. Should I use LVL or Hardwood for my deck?
    By LotteBum in forum DECKING
    Replies: 3
    Last Post: 3rd May 2007, 09:41 PM

Tags for this Thread

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •