Planing a Deck around a above ground pool - Stirrup Issues
Hi i am planning a deck around a new pool (above ground).
The deck will be 9M * 2m AND 1.4 high - See attached design
I am planning to use:
Posts = 100*100 HW
1500 centers
Bearers = 125*50 HW
Joists = 125*50 HW
Deck = Merbeu 90*19
Issue:
I intend to use Gal Post Anchor (Stirups) - due to Brisbane Termites
How deep do i need to have the footings?
How deep into the footing do the Anchors have to go?
I have an issue that 5 of the post loctaions are over storm water (ONLY 300 DEEP) If i move them then one way I am over sewerage (ONLY 600 DEEP), and cannot move them the other due to the edge of the pool.
What are my options ?
Thx
-
24th April 2007, 10:57 AM #2Senior Member
- Join Date
- Oct 2005
- Location
- newcastle
- Posts
- 216
hiya - you do seem to have a problem......
now short of having an engineer come out and charge $500 for a simple footing design, here's what i would do (keep in mind I am not an engineer, and take no responsibility for anybody stupid enough to follow my advice ! )
I would aim for a wider than normal footing that spreads the load. Secondly I would dig between the pipes as deep as i could go - prefereably down to natural undisturbed ground, and also on either side of the pipes - the idea is that the weight bearing is on the ground below the pipes, and the concrete simply surrounds the pipe. It maybe even possible to go deep between and then spread out the slab above the pipes at only 200mm thick, as long as the post is above the deep section..
Final option is to go really shallow, above all pipes, but re-enforce the footing with steel - this gives no lateral strength, but still provides bearing ability - it is after all a pool deck, and not a car deck! Plenty of times you will see a deck for people simply attached to a 100mm reinforced slab floating on sand (existing).
-
24th April 2007, 06:03 PM #3
Your bearers should be 125 x 70 minimum according to my tables. Generally (as far as it is possible to gheneralise without gettting soil tests etc) your footings would be 450 dia. x 600 deep minimum. Other than redesigning your deck with longer spans to avoid the pipes I can't see any good alternatives.
Mick"If you need a machine today and don't buy it,
tomorrow you will have paid for it and not have it."
- Henry Ford 1938
-
24th April 2007, 10:35 PM #4
Hey Decker, A deck over 1m often needs council approval and a DA, under chich circumstances you would we given some advice by them on what to do. Generally they will not let you built over a sewer and footings will have to bear below the sewer.
Cheers
Pulse
Similar Threads
-
Pool Deck Advice
By mcchaddy in forum POOLS, SPA & WATER FEATURESReplies: 1Last Post: 30th January 2007, 12:53 PM -
deck on ground help pls
By browny000 in forum DECKINGReplies: 12Last Post: 7th January 2007, 12:34 PM -
pool deck stair ideas
By lmcmali in forum POOLS, SPA & WATER FEATURESReplies: 0Last Post: 6th June 2006, 05:06 AM -
Planning a Pool Deck
By Clive McF in forum DECKINGReplies: 6Last Post: 14th May 2006, 12:35 AM -
deck footings into rocky ground
By wigfam in forum DECKINGReplies: 4Last Post: 13th May 2004, 06:12 PM
Bookmarks