    Default Powerpoints near the sink- how close?

    Hi There,

    I have moved into a new unit and have noticed the powerpoints are extremely close to the sink.

    They are approximately 100mm from the edge of the bowl, and about 100mm above the counter. The distance from the spout would not be more than 200mm. Can anyone tell me if this is in accordance with the electrical safety standards. The unit is in Sydney.

    Thanks

  2. #2
    Join Date
    Jan 2007
    Location
    Katoomba NSW
    Posts
    332
    Post Thanks / Like

    Default

    Antcom,
    They are deffinately not in accordance with AS3000.
    The power point should not be installed within 150mm from the edge of the bowl and 400mm above the bowl/bench surface.

  3. #3
    Join Date
    Aug 2002
    Location
    Boyne Island, Queensland
    Age
    52
    Posts
    176
    Post Thanks / Like

    Default

    Quote Originally Posted by NCArcher View Post
    The power point should not be installed within 150mm from the edge of the bowl and 400mm above the bowl/bench surface.
    Unless they are protected by a RCD with a residual current rating not exceeding 30mA; and
    have automatic switching and are incorporated in a shaver supply unit complying with AS/NZS 3194; or
    it's in a cupboard that's going to stay shut.

    Well that's what AS/NZS 3018:2001 says.

    AS3000:2000 says,

    the bit about auto switching and shaver supply; or
    protected by RCD; and
    in a cupboard.
    Somewhere in the translation from AS3000 to AS3018 the ands and the ors have been swapped.
    Dan

  4. #4
    Join Date
    Oct 2005
    Location
    Emu Plains
    Posts
    409
    Post Thanks / Like

    Default

    Quote Originally Posted by Dan View Post
    the ands and the ors have been swapped.
    That happened to me once and I ended up rowing in completely the wrong direction.
    Retired member

  5. #5
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    67
    Posts
    1
    Post Thanks / Like

    Default

    Quote Originally Posted by Felder View Post
    That happened to me once and I ended up rowing in completely the wrong direction.
    Ah well in that case you would have ended up where you were supposed to be going not where you thought you were going.
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

Similar Threads

  1. Installing undermount sink
    By vGolfer in forum KITCHENS
    Replies: 1
    Last Post: 3rd December 2006, 10:40 AM
  2. House renovation - new external sink to sewer
    By Scan_Fan in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 3
    Last Post: 7th November 2006, 09:26 PM
  3. Installing Kitchen Sink
    By blt in forum KITCHENS
    Replies: 6
    Last Post: 14th August 2005, 03:57 PM
  4. All but the kitchen sink
    By marineman in forum KITCHENS
    Replies: 16
    Last Post: 5th February 2005, 04:22 PM

Tags for this Thread

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •