Results 1 to 15 of 15
  1. #1
    Join Date
    Nov 2006
    Location
    Melbourne
    Posts
    8

    Default Height regs of Meter Box's?

    Does anyone know how high a meter box has to be?

    I'm currently building a new house and they put the meter box in ridiculously low so I asked them to put it higher and they did, but only about 200mm. It is now 1375mm from the top of the slab to the top of the meter box and still looks too low....

  2. #2
    Join Date
    Apr 2006
    Location
    Wagga Wagga
    Age
    71
    Posts
    53

    Default

    Hello Bronson,Here in Wagga we set the boxes at a height of two metres from the finished path(that is to top of box).So when we (bricklayers)set out for them we usually consider the finished concrete path height as sometimes you might have to put the box in at a higher measurement to allow for it.I've seen plenty too low and I think they look odd when put in that way.Regards Terry

  3. #3
    Join Date
    Sep 2004
    Location
    Strzelecki Ranges Victoria
    Posts
    395

    Default

    The last info I have is between 1500 & 2000 above finished ground level to the top of the panel but I don't know if this varies - don't see why it should. There are also requirements on clearances etc.
    Peter Clarkson

    www.ausdesign.com.au

    This information is intended to provide general information only.
    It does not purport to be a comprehensive advice.

  4. #4
    Join Date
    Aug 2003
    Location
    Pambula
    Age
    59
    Posts
    5,026

    Default

    I don't know what it has to be, but ours is about 1800 from ground level, so when the lid is propped open, most people can walk under it without hitting their head. You want it at a height so that you can look at the inside of it without getting down on your knees. Your's sounds too low to me. Did the sparky put it in?

  5. #5
    Join Date
    Aug 2006
    Location
    Australia
    Posts
    66

    Default

    I agree with the 1800mm (from ground to top of box), thats usually the height we install all ours at. The wiring rules state that the main switch should not be located higher than 2m from the ground or platform.

  6. #6
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    66
    Posts
    1

    Default 900mm Min, 2M Max.

    Taken from
    AS/NZS 3018:2001 Electrical Installations - Domestic installations.

    (I'd get in the poo if I copied it & posted it here.)

    A minimum to the bottom of the switchboard is 900mm & maximum to the top is 2m with a minimum of 60mm clearance in front of the switchboard.
    Anything below it must not stick out more than 600mm past the switchgear in the switchboard.
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

  7. #7
    Join Date
    Nov 2006
    Location
    Melbourne
    Posts
    8

    Default

    Thanks for all of the responses guys. I spoke to my building supervisor and he said he would go check it out. He thought that they were usualy around the 1500 mark, but I think 1800 would be better.

    Thanks for the AS specs Cliff!!!

    I'll let you know how I go.

  8. #8
    Join Date
    Apr 2006
    Location
    Wagga Wagga
    Age
    71
    Posts
    53

    Default

    Funny how the building supervisor had to check it out.You'd almost think he'd have some idea about it.The boxes we use are 600mm*600mm so as I said we like to go the highest legal measurement, as when you take 600mm from 1500mm I think it's far too low to the bottom of the box and looks wrong if nothing else.Regards Terry

  9. #9
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    66
    Posts
    1

    Default

    Quote Originally Posted by Terry1 View Post
    ...when you take 600mm from 1500mm I think it's far too low to the bottom of the box ....
    Nope, that would make the bottom 900mm & just legal if it is a domestic installation, but yeah, it looks silly.
    Cliff.
    If you find a post of mine that is missing a pic that you'd like to see, let me know & I'll see if I can find a copy.

  10. #10
    Join Date
    Jan 2006
    Location
    Glen Waverly
    Age
    47
    Posts
    17

    Default

    In Victoria the Service installation rules (SIR's) are what governs the maximum and minimum heights of meter mounting. Clause 8.11.1

    The maximum height to the top edge of the meter panel is 2.1m above floor or ground level.

    The minimum height to the bottom edge of the meter panel is 1.0m above floor or ground level.

    AS3000:2000 clause 2.8.3.3.2 governs the maximum main switch height.

    Assuming the metering enclosure also is housing the main switchboard "Generally" The only other restrictions are the maximum height of the main switch which is 2.0m above floor or ground level.

  11. #11
    Join Date
    Nov 2006
    Location
    Melbourne
    Posts
    8

    Default

    Just an update......

    Went to the house last night and although the meter box is still the same height, the bricklayers pushed the meter box back in toward the inside of the house and have bricked a spot for it to go. It will be a little under 2M from top of slab to top of box!!! I'm extremely happy with this.

    I'm not sure if the sparky has seen it yet but I don't think he has much choice now.

  12. #12
    Join Date
    Oct 2003
    Location
    Kentucky NSW near Tamworth, Australia
    Age
    86
    Posts
    1,067

    Default

    Don't know if it is a local rule because some Electical Suppliers do have local rules and here you couldn't have a main switch any higher than two metres from the ground, nothing about the height of the box.

    When I put my meter box on the pole I was a fraction too high with the main switch and the county council inspector told me just to pour a block of concrete to stand on.

  13. #13
    Join Date
    Sep 2004
    Location
    Strzelecki Ranges Victoria
    Posts
    395

    Default

    Quote :"The maximum height to the top edge of the meter panel is 2.1m above floor or ground level.

    The minimum height to the bottom edge of the meter panel is 1.0m above floor or ground level."end Quote. [Ican't work out how to do that]

    ?? so what is the height of a meter panel ??
    Peter Clarkson

    www.ausdesign.com.au

    This information is intended to provide general information only.
    It does not purport to be a comprehensive advice.

  14. #14
    Join Date
    Apr 2006
    Location
    Adelaide
    Posts
    32

    Default

    Just to add to the confusion.... The latest switchboards made by B&R here in SA have the switch-panel at the bottom of the board. There was an article in the latest newsletter from the Technical Regulator here in SA covering the subject of panel location within the switchboard, makes for interesting reading.....see page 4 of
    http://www.energysafety.sa.gov.au/im...RR18_Nov06.pdf

    B&R link here,
    http://www.hagerbr.com.au/files_down...Enclosures.pdf

  15. #15
    Join Date
    Apr 2006
    Location
    Wagga Wagga
    Age
    71
    Posts
    53

    Default

    It was interesting to see all the different types of meterboxes that they make in SA we only ever use the one type here.The measurements of the standard one used here is 600mm*600mm.They are made to suit brickwork (seven courses high and two and a half bricks wide)If you set it out on top of 16 courses (which is approx 1372mm)the top of the box is then 1972mm which is close to the our accepted limit.This seems to look and work just right (as far as reading the meter goes etc.)Regards Terry.

Tags for this Thread

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •