    Default How much water ?

    Hi all, just an enquiry.

    I have a building and the roof area is 52 square meters. Question is how big of a drainage pipe system would be required for the roof size. It currently has a ninety eight mill earthenware pipe which runs under the building for about 12 meters and is in need of replacement. I was hoping I could push some ninety mill
    sewerage line or some stormwater pvc through the existing pipe.

    All ideas welcome

    Kind regards mike

  2. #2
    Join Date
    Jan 2005
    Location
    Newcastle/Tamworth
    Posts
    416

    Default

    Mick visit the lysaght web site, they have a design manual that matches the applicable standard. Basically you design the drainage based on a rain intensity peak every 20 years. In Tamworth it is about 160mm/hr. There are tables where you read off the area and the gutter cross sectional area. Then finally the size of the downpipe.

    Cheers
    Pulse

Similar Threads

  1. Rain Water
    By gdf26562 in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 3
    Last Post: 20th September 2006, 04:31 PM
  2. Hot water goes cold in the pipes: what to do
    By silentC in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 31
    Last Post: 19th July 2006, 10:16 AM
  3. Gas hot water heaters
    By Bob Willson in forum NOTHING AT ALL TO DO WITH RENOVATION
    Replies: 28
    Last Post: 29th March 2005, 12:16 PM
  4. Water Crisis!!
    By Tikki in forum NOTHING AT ALL TO DO WITH RENOVATION
    Replies: 18
    Last Post: 19th November 2004, 03:51 PM
  5. bad water
    By capedcrusader in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 9
    Last Post: 24th July 2004, 09:11 AM

Tags for this Thread

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •