    Unhappy 12 Volt Halogens Earth??

    Ok.. Scenario,3 wire cable active neutral and earth going into a 240 to 12 volt transformers which feed the 12 v halogens. There is a provision for the ac but nothing for the Earth. It cant feed into the transformer so does it stay floating? (doubt it) or taped back onto the cable? whats the go. my electrician recons the previous owners shouldnt have done it that way, ok i agree where does the earth wire end up?? No bare copper should be visible.

    he didnt tell me how its to be done as he wants 50 bucks a light to "fix" if there is anything wrong in the first place. At the moment the green earth wire is taped back onto the cable

  2. #2
    Join Date
    Jan 2005
    Location
    Newcastle/Tamworth
    Posts
    416

    Default

    Your sparky is right, it is not the best way. One way is to have a loop at each light and strip the white sheath, leaving the insulation undamaged. Then strip the active and neutral and wire into the transformer. The earth is then continuous and undamaged. Technically the sheath protection should be reinstated with electrical tape. The other option is to connect the earths with a two screw terminal and wrap with electrical tape. At the last fitting, cover with a screw terminal and tape with electrical tape.

    Cheers
    Pulse

  3. #3
    Join Date
    Aug 2006
    Location
    Bentleigh
    Posts
    2

    Default

    Thanx Pulse, thats exactly what another electrician i asked today said.

    Im giving this guy the flick anyway cause of his smart #### attitude .

    im sure another electrician will appreciate the work



    cheers

    Paul

  4. #4
    Join Date
    Jan 2005
    Location
    Newcastle/Tamworth
    Posts
    416

    Default

    Yep, I've got no time for people who aren't helpful. Some tradies don't realise that a good DIYer will make their job easier, not harder

    Cheers
    Pulse

  5. #5
    Join Date
    Jun 2006
    Location
    the 'burn
    Posts
    118

    Default

    Some tradies don't realise that a good DIYer will make their job easier, not harder
    some DIYers don't realise that they should stop trying to save a buck when it comes to electricity

  6. #6
    Join Date
    Aug 2005
    Location
    South Australia
    Age
    77
    Posts
    117

    Default

    Q. What's black, crispy and hangs off your light fitting?

    A. DIY, non-qualified electricians.

  7. #7
    Join Date
    Oct 2005
    Location
    newcastle
    Posts
    216

    Default

    Quote Originally Posted by Eddie Jones View Post
    Q. What's black, crispy and hangs off your light fitting?

    A. DIY, non-qualified electricians.
    LOL! More like an extremely stupid person - qualified or not - see darwin awards.

    Dont most electrocutions occur to people doing nothing at all with electricals - live roofs, live steel framing, kitchen appliances etc - generally things that werent grounded untill someone leaned on them (sometime after a rat went to rat heaven)

Similar Threads

  1. Shocking question!
    By journeyman Mick in forum NOTHING AT ALL TO DO WITH RENOVATION
    Replies: 48
    Last Post: 7th May 2007, 10:03 PM
  2. Connecting the earth?
    By Pulpo in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etc
    Replies: 16
    Last Post: 7th February 2006, 10:22 AM
  3. Help needed with Google Earth
    By echnidna in forum NOTHING AT ALL TO DO WITH RENOVATION
    Replies: 22
    Last Post: 17th December 2005, 08:23 PM
  4. Advantage of living on Earth
    By rod1949 in forum JOKES
    Replies: 5
    Last Post: 26th July 2005, 04:16 PM
  5. The worlds largest earth mover (apparently)
    By Wayne Davy in forum NOTHING AT ALL TO DO WITH RENOVATION
    Replies: 9
    Last Post: 7th June 2005, 04:41 PM

Tags for this Thread

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •