3rd April 2006, 04:50 PM #1
Wood heater not burning properly ??
How is ya guys.
We have a Norsman inbuilt wood heater ,3 speed fan , 20 yrs old [ guess ] .
Sometimes it throws out so much heat we need to open doors . Other times we can get any heat at all out of it , more often the later .
Has anyone got any idea as to how to get it running consistantly or what might be wrong with it ?
Doesn't seem to be the type of wood as we chuck on all sorts and it seems to roar drawing when it's firing . lt just either heats really well or it doesn't , abit like me it all seems to depend on how it feels on the day !
Cheers.
MB.
-
3rd April 2006, 04:58 PM #2
Get the flue swept.
bet it goes well on windy days.
No wind no heat.p.t.c
-
3rd April 2006, 05:14 PM #3
The easiest way to clean the flue is to drop a length of rope down the flue, attatch some chicken wire to the top bit of rope. ( you did leave some out the top, and not drop the whole rope down the flue didnt you?
).
Go inside and pull the chicken wire down, job done.
As PTC has said windy days make it draw better, IMHO it has nothing to do with a blocked flue, if its blocked smoke will bellow out into you room.
Windy days just make it burn better.
We get the same situations here, it might be the wood, some loads of wood definatly burn better.
Al
-
4th April 2006, 09:58 AM #4
Thanks for that.
Not a bad cleaning idea Al , didn't wanna lash out on a brush .
Anyway l took it all to bits this morning see if l can find any other prob's so l'll clean it all inside out while l'm at it and see if it helps .
Al are they a good heater though ?
Only been here 6 mths so we haven't been through a winter with it yet !
Noticed once l had everything of it it's virtually just a free standing heater with a casing added to fit in the wall . Bloody tempting to take it right out and freestand it instead , should get heat then what do you think ?
Cheers
MB
-
4th April 2006, 10:14 AM #5
Use seasoned, dry wood.
If it works good some days and not others, eliminate as many variables as you can, record those you can't (wind speed and direction)
I think the biggest problem people have with combustion heaters is using green wood and not ever getting a decent fire going. Usually results in a chimney fire down the track as all the tar etc deposits in the chimney, and one day the whole lot goes up.
We gave it away because of the difficulty in getting good wood, and the choking stink in the neighborhood from ours and others fires. If you enjoy a morning or evening walk in winter, you will know what I mean, somedays all the smoke seems to decend to ground level and combine with the moist air in a way that leaves an obnoxious sooty smell about the place...
woodbe.
-
4th April 2006, 05:40 PM #6
Originally Posted by masterblaster
We got the gas connected last year, but when I priced appliances I nearly fell over.
$2500 for a gas log lookalike. :eek: Then the plumber etc.
We'll stick with wood I think..
Al
-
4th April 2006, 06:54 PM #7
Hi All This is my first post, but we've had wood fires for the last fifty years plus, so I hope I've learned something.
IMHO the cause of the Norseman burning unevenly is most likely due to:
* Either, smoke/air is not getting out properly due to unclean flue,
* Or, fresh air not getting in easily due to build up of fine white wood ash behind air inlet vents.
The latter is the most likely and is awkward to fix due to poor visibility and poor access to inside of air vents.
First you must unclip all external covers to maximise access to the innards of the heater. We made a thin nozzle extension for the vacuum cleaner and poke it through the vent holes. We also use a piece of wire to dislodge caked ash, push some ash into firebox and move other ash within reach of vacuum. We have also used compressed air to blow ash into firebox.
Remember ash is very light and messy.
Hope this helps
Graeme
-
4th April 2006, 08:14 PM #8
Originally Posted by GraemeCook
-
4th April 2006, 08:36 PM #9
Oh, yes. I forgot about the mess while I was reminiscing about how romantic it was to watch the flames through the glass while sipping on a nice vintage port and feeling all cosy and warm.
Thank god for reverse-cycle...
woodbe.
-
4th April 2006, 09:04 PM #10
Thanks Graem l reckon your onto something . Tomorrow we'll vac through those vents while it's in bits .
Hey Al yeah we got a nice gas heater given to us so it's just sittin here right now . First the plumber costs and then we are on bottle gas which they reckon use easy a bottle every 3 wks to a mth- $80 bucks , so it's still sitting there .
Now this is gonna confuse things but Woodby what do you think of reverse cycle and how much does that cost to run ?
This house has the wiring and holes all ready for reverse cycle because they took it out when we bought the house.Thier's was an old rattler so we didn't want it when they tried to charge us an extra 2 grand to leave it in .We thought there's no way they'll take that out and thought we'd get it for nothin anyway but the bugars took the lot .
cheers.
MB
Originally Posted by GraemeCook
-
4th April 2006, 10:23 PM #11
Originally Posted by masterblaster
Anyway, ours is a big ducted system that uses water pumped around underground instead of the air outside. I think they call it 'geothermal heat pump' they reckon it gets a 5:1 output:input ratio versus a 3:1 for the air interchange systems. It seems to keep the place a comfortable temperature, but unfortunately there is no outlet in the workshop
Cost to run? Heaps, but it IS a big house. When we installed it, we had a quote for ducted gas heating that was going to cost more to run than we are paying for heating AND cooling now, per year. That was 10 years ago. So we are getting the cooling for free...
These days, we'd probably go for several of those split systems with the confusing remote controls and regular breakdowns. I hear that the efficiency of them has improved out of sight, but there is no direct comparisons available so it might just be marketing-speak.
Anyway, I guess this is a long way of saying that there is no easy way of comparing burning wood with reverse cycle, but if you record how much wood you burn in a year, you might be able to make an informed decision about your own situation. Bear in mind that the electricity you use in a reverse cycle system probably comes from a coal-fired generator, so who knows what the bottom-line efficiency really is
Hope I haven't confused you, I know I am...
woodbe.
-
5th April 2006, 12:06 AM #12
MB, my sister's house in Horsham had a Norseman built in woodheater and it was a ripper, belted the heat out.
We have an inbuilt Coonara with a pretty long flue, I find it can be a bugger sometimes to get it to draw when lighting it. I just get the newspaper & kindling set up in the firebox, then push a couple of sheets of newspaper in above the baffle. Light the couple of sheets first, then the main fire. The sheets burn up quickly and get the column of air in the flue moving upward, and the fire starts better and gets it drawing straight away.
Works for us, hth.....cheers......Sean, love woodheating, hate chasing wood
The beatings will continue until morale improves.
-
5th April 2006, 12:37 PM #13
Originally Posted by Auld Bassoon
Ash is difficult to remove from inlet vents. To minimise mess in inside the house we closed the firebox door and held rags around the compressed air nozzle and heater inlet vent - partially effective. However, a "snow storm" went up flue and all over roofs, gardens, etc. Neighbours are still wondering who donnit.
Cheers
Graeme
-
5th April 2006, 01:24 PM #14
Originally Posted by woodbe
We have been looking at installing a ducted heat pump and have been impressed by the efficiency and quietness of geothermal units. However there is not a lot of information in Australia on domestic size units.
Could you provide any information or leads that may assist in our information gathering process and eventual decision. For example, what brand do you have, who are its competitors, frank opinions, etc.
Basically I am getting tired of chopping firewood, spiders and ash, and of retreating into two rooms in winter.
* LPG is too expensive and inconvenient,
* Natural gas is not available yet where we live,
* Conventional electricity is expensive to run,
* Underfloor heating is not compatible with wooden floors,
* Split unit heat pumps are visible, noisier and cost the same as ducted once you heat more than three rooms.
Any advise or insights will be much appreciated.
Incidentally, I have read that in Sweden the COP (efficiency) of 8 has been reached for geothermal heat pumps coupled to a hydronic in-house system (heated pipes in a concrete floor). Incredible.
Cheers
Graeme
-
5th April 2006, 02:41 PM #15
Well, it's a long road you are looking down...
We lucked onto our system by sniffing around the Energy Information Service here in Adelaide when we decided we needed heating (we had none when we moved in, previous owner was a martyr or something). Anyway, after giving them the plans and aspect of the dwelling, the EIS gave us a list of possible options and where to get them. Top of every list was geothermal, but they gave no contact. When we asked why, the response was "no-one will pay for them, because they are too expensive"
Having a large home, and wanting to stay long term, we decided to see how much more it was, and if it would payback over a few years. The story checks out, and we bought one. At the time, the extra cost of geothermal versus normal heatpump was something like 30%, and the payback on that was quoted at 3-5 years. Frankly, we have no idea if we achieved payback because we have nothing to compare against, but I believe we are better off than if we went for the normal heatpump, and it's certainly cleaner and a lot less hassle than a slow combustion heater.
Last I spoke with the dealer, he said that their main market in Australia has turned out to be commercial systems and large developments where the AC is planned from the ground up, like apartment buildings etc. Joe Average homeowner has basicly rejected the concept in favor of the quick fix split system. (can't really blame them for that, it's a lot of work to plan a geo system)
In the US, you can buy geothermal AC units and install them yourself, just like you can do a split unit here if you have a mind to. They do stuff like throw the 'loop' (the water loop that exchanges the heat) in a local lake or river, which would probably be illegal here.
Our system lives down in the basement, and our loop is installed in a series of bore-holes drilled into the rock under our back yard.
This is the mob in the US that made it:
http://www.waterfurnace.com/content....ntial&page=rez
There are others. I don't know who sells them here now, lost track of them, sorry.
woodbe.
Similar Threads
-
Rayburn wood burning stove
By davo453 in forum NOTHING AT ALL TO DO WITH RENOVATIONReplies: 19Last Post: 12th December 2011, 09:02 PM -
Can you angle a wood heater flu ?
By masterblaster in forum HEATING & COOLINGReplies: 10Last Post: 17th February 2006, 08:58 PM -
Freestanding fireplace
By wooded in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etcReplies: 3Last Post: 22nd November 2005, 02:45 PM
Bookmarks