3rd March 2008, 12:10 PM #1
Gas and electricity don't mix
Just made the big move up to Brisbane, and am about to move into a new house. The house uses 45KG gas bottles. At least it will once this problem is cleared up.
A guy came out to install the bottles, but took one look and refused. He told me the powerpoint for the split AC system was too close to the gas bottles, and would have to be moved.
So I'm sure he's right, and the power point will have to be moved. My questions are: What is the minimum distance, and why didn't either of the installers pick up the problem? Surely there is legislation which clearly states requirements?
-
3rd March 2008, 12:22 PM #2
If the gas bottle connection was installed before the split system was then the refrigeration mechanic would have had to know the gas requirements. Unfortunately the gas regulations would be outside the scope of knowledge of the fridgie. This is why larger jobs have detailed drawings with the locations for all the services clearly identified.
Mick"If you need a machine today and don't buy it,
tomorrow you will have paid for it and not have it."
- Henry Ford 1938
-
3rd March 2008, 01:26 PM #3Cheers.
Vernon.
__________________________________________________
Bite off more than you can chew and then chew like crazy.
-
3rd March 2008, 02:06 PM #4
We had a similar situation this week when we were told the gas suppliers would not fill our gas bottles because our recently fitted gas hot water service was too close to the bottles.Rang the plumber who installed the hotwater and he came around and raised the unit, at his expense.
rang the gas supplier and they came and inspected the job and told me they still would not fill the bottles because the power point that was installed at the same time as the hotwater was too close to the gas bottles.I ended up moving the power point myself and all is well.
The regs stated (I think) that any ignition point , in our case the h/water and power point have to be a minimum of 500mm from the gas bottle valve.
Hope this helps. Cheers StevenThe hurrier I go, the behinder I get.
-
3rd March 2008, 02:52 PM #5
The guy who came out should have told you how far everything needs to be from the bottles. the entry point I presume.
-
3rd March 2008, 02:56 PM #6
For gas bottles filled on site, the unit must be 3m or more away or 1/2m above For replacement gas bottles, the unit must be 1.5m or more away or 1/2m above
-
3rd March 2008, 07:59 PM #7
airmen is right, except for the insitu fill cylinder location, i thought was 3.5mts at the base.for exchange bottles its 1.5 from base, unless the code has changed.
-
3rd March 2008, 08:47 PM #8
Exchange cylinders:
From the base of the cylinder its is a radius of 1500mm from centre,
From the centre of the valve it is 500mm in height and a radius of 500mm.
In-Situ Fill:
From the base of the cylinder it is a radius of 3500mm from centre,
From the centre of the valve it is 500mm in height and a radius of 1500mm.
And lets not forget the 1m rule for openings into a building, vents, drains etc.Plumbers were around long before Jesus was a carpenter
-
4th March 2008, 02:12 PM #9
Thanks everyone who replied.
The good news is the builder got it sorted out within 2 days, I didn't have to threaten or even yell at anyone.
Just another thing to be aware of if getting any work done around gas bottles I guess. Don't count on the sparkie to know the rules, he may have never come across this situation before.
Similar Threads
-
Electricity Mains
By Cobber in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etcReplies: 17Last Post: 16th February 2008, 01:17 AM -
3 phase electricity
By trenyboy in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etcReplies: 9Last Post: 20th August 2007, 10:46 PM -
Big Electricity Bill
By silentC in forum PLUMBING, ELECTRICAL, HEATING, COOLING, etcReplies: 77Last Post: 29th March 2007, 08:30 PM -
Electricity usage??
By ozwinner in forum NOTHING AT ALL TO DO WITH RENOVATIONReplies: 43Last Post: 31st December 2005, 02:17 PM
Bookmarks