Results 1 to 11 of 11
  1. #1
    Join Date
    Jul 1999
    Location
    Glen Iris, Vic, Australia
    Posts
    314

    Default Please help with second opinion foCentral Heating Repair Diagnosis - before replacing

    Please help with second opinion for Central Heating Repair Diagnosis - before replacing

    Last year or two about this time a repairman sand blasted the burners and all worked until recently.

    Getting a strong insistence from the accountant
    that before buying a new unit
    I sould I make sure.

    So
    Pilot Flame was going out.
    When pilot lit manually
    The heater would flame on and work properly.

    Until over night the pilot light would be off again.

    Repairman came out cleaned everything.
    pilot light was on and stronger than before.
    Repairman left with both working.
    Controller working on and off.

    everything worked the next day.

    Buth this morning
    Pilot light stayed lit overnight
    but wouldn't flame on.

    Hit the reset button.
    And flame on.

    Any help other than just replacing would be much appreciated.

    Thanks in Advance.
    Thanks,
    Barry G. Sumpter
    May Yesterdays Tears Quench the Thirst for Tomorrows Revenge

  2. #2
    Join Date
    Sep 2005
    Location
    Bendigo
    Age
    60
    Posts
    237

    Default

    Make?
    Model?
    Controller?
    System / error messages?
    Age of unit?

  3. #3
    Join Date
    Jul 1999
    Location
    Glen Iris, Vic, Australia
    Posts
    314

    Default

    Thanks for the reply.

    It's been running properly over the last two nights.
    But not working this morn.

    I've received the goahead if we can't figure it out.
    It's worth 4k to make sure.

    Make? : Airite
    Model? Model: 4955
    iScreen Shoter - 20240727112627843.jpg
    Controller? Brivis
    IMG_5974.jpg

    System / error messages? None
    Age of unit? 30+ - Certain original parts not available.
    “So the flame is going to be the gas valve buddy and you cannot get the gas valve any more unfortunately“

    As a last attempt We'll be replacing the Thermocouple Saturday avo.
    Unless otherwise suggested.

    Thanks in Advance.
    Attached Images Attached Images
    Thanks,
    Barry G. Sumpter
    May Yesterdays Tears Quench the Thirst for Tomorrows Revenge

  4. #4
    Join Date
    Sep 2005
    Location
    Bendigo
    Age
    60
    Posts
    237

    Default

    Googling the brand and model reveals nothing, have seen similar issues with other manufacturers and the manual will often give you a good breakdown of the start and run processes.

    With a pilot flame as opposed to surface ignition it probably is going to come down to gas valve or flame sensor.
    If there are limited parts all you can do is replace the ones that are available and if its deeper than that then replacement is probably the best option.

  5. #5
    Join Date
    Jul 1999
    Location
    Glen Iris, Vic, Australia
    Posts
    314

    Default

    Champion! Many thanks.
    Thanks,
    Barry G. Sumpter
    May Yesterdays Tears Quench the Thirst for Tomorrows Revenge

  6. #6
    Join Date
    Jul 1999
    Location
    Glen Iris, Vic, Australia
    Posts
    314

    Default

    Wonder if replacing that Gas heater with an electric heater is viable.
    Thanks,
    Barry G. Sumpter
    May Yesterdays Tears Quench the Thirst for Tomorrows Revenge

  7. #7
    Join Date
    Jul 1999
    Location
    Glen Iris, Vic, Australia
    Posts
    314

    Default

    Removed incorrect comparison query.
    Thanks,
    Barry G. Sumpter
    May Yesterdays Tears Quench the Thirst for Tomorrows Revenge

  8. #8
    Join Date
    Sep 2005
    Location
    Bendigo
    Age
    60
    Posts
    237

    Default

    The motor in the gas heater will not be 600kW, dont care what the ID plate says it is wrong.
    The power rating from the ID plate is 240v 5.0A, = 1200w so maybe 600W motor ?
    In a gas heater the motor is for moving air and does not add to the heating power, you need to compare the heat output of the gas heater that will be kW, Mj or maybe BTU but you would need to get the specs for an Airite EX110 from the manufacturer.

    The 14kW electric heater is the heating output from the unit, it is the basis of the size of the unit needed. In simple terms the larger the area to be heated the more kW's required.
    You will find plenty of online calculators if you search
    https://www.ozaironline.com.au/pages...ing-calculator
    https://www.frozoneair.com.au/splitguidepage

    Of course with ducted heating it is also about the duct design and efficiency, zoning and maximum / minimum registers open will all come into the calculations.
    If you are looking to replace gas ducted heater with electric ducted then factor in complete duct replacement. IE complete new install.
    Reason is that electric ducted is a lower heat and higher volume of air that is used, the ducts and vents used for the gas will most likely need to be increased in size.

  9. #9
    Join Date
    Jul 1999
    Location
    Glen Iris, Vic, Australia
    Posts
    314

    Default

    Thanks heaps droog. Sincerely appreciated.
    Got the nix on our 1920s Edwardian.
    The asthetics would not be appealing.
    5 heads max on electric up grade.
    We have 13 outlets.

    Back to Bonaire MB530kw external as a replacement.
    Thanks,
    Barry G. Sumpter
    May Yesterdays Tears Quench the Thirst for Tomorrows Revenge

  10. #10
    Join Date
    Jul 1999
    Location
    Glen Iris, Vic, Australia
    Posts
    314

    Default

    Just had a quick flash of an idea stepping out the door.
    This unit is being replaced with the MB631.

    Should I salvage the fan out of the old one.
    As it blasts air thru 13 ducts.

    I could use the fan as a dust extractor for the shop or maybe a dust extraction table top.

    Any thoughts anyone?
    Thanks,
    Barry G. Sumpter
    May Yesterdays Tears Quench the Thirst for Tomorrows Revenge

  11. #11
    Join Date
    Sep 2005
    Location
    Bendigo
    Age
    60
    Posts
    237

    Default

    Check the type and construction of the fan.
    For ventilation yep go for it, dust extractors have a solid construction impeller as bits of timber will destroy a lesser construction designed to move only air.

Similar Threads

  1. Fence repair - your opinion on 2 methods
    By Joynz in forum FENCES & SCREENS
    Replies: 7
    Last Post: 17th May 2024, 11:51 PM
  2. HELP Ducted Heating Unit Repair - Melbourne
    By MLU in forum HELP! "I've fallen and can't get up."
    Replies: 0
    Last Post: 18th May 2020, 12:16 PM
  3. diagnosis
    By underfoot in forum JOKES
    Replies: 0
    Last Post: 25th March 2008, 05:32 PM

Bookmarks

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •