I recently installed 15 amp power to my tool cupboard so that I could hide my compressor in there. It used to work fine when it was plunked in the middle of my workshop but it has been blowing its condensers lately, and at $30 a pop I don't want to replace them again.
The details are:
The line used to be 5 metres long and worked OK.
I extended the line by 7 metres to put it in the tool cupboard.
The wire I used is stranded copper wire with the following dimensions
Positive wire: 5 strands of .65mm dia
Negative wire: 7 strands of .65 mm dia
Earth wire: 7 strands of .65 mm dia
The compressor also has a 2 metre 15amp lead on it
The motor is 240v 3 hp (or so I am told, the plate is illegible) and (supposedly) draws about 40 amps on startup. :(
The condensers are 108-140 MFD 220v.
The question is, are the wires heavy enough to support this load and enable the condensers to do their work without melting?
When they blow, they make a reasonable sized bang and the room fills with smoke. :eek:
If they aren't heavy enough, what size should I be using for a run of that length?