12th May 2008, 03:02 PM
G'day all,
I’ve just finished electrician A-grade. Someone is built the new 2 house (front and back) and asked me for information as they will supply parts and I’ll do the work. Since I’ve got hand over from my master as he is oversea for 5 months holiday, he will approve when he’s back. I’ve asked around but still need some advice. This is how I would do:
<o:p> </o:p>
For back house, 3-phase underground cable from the Pit to the electrical meter is 5 meter, so SDI cable would be 16mm2; 3 x 7meters of white-red SDI cable and 7 meter of white-black SDI cable. Front house, 240V 2 x 7m white-red and white-black cable. Is this correct? Can I make a loop before the supply meter to save front house cable? These will run under 2 x 70mm orange conduit, 600mm deep for 2 houses,
<o:p> </o:p>
Front house, from electrical meter to switchboard is 20m, same SDI 16mm2 cable, so 2x20 m white-red and white-black cable. Back house is 40m, so 3x40m white-red and 40m white-black SDI cable. Still run with 70mm orange conduit. Can I use 3-phase PCV orange cable, 4core and earth 10mm2 for the back house?
<o:p> </o:p>
If I run out of white-black SDI cable, can I use white-red SDI cable instead?
Should cable insert into conduit then put underground OR conduit first then pull cable later? I will ask someone to inspect the conduit before fill the soil.
<o:p> </o:p>
Back house, they will have 1 small (2.5kW) and 1 big (7.1kW) air conditioning, can I use 2.5mm2 cable to connect or has to be 4mm2, 1 phase each connection?
<o:p> </o:p>
Front house is ok as only 1 phase, but back house is a bit complicate. Do you have any ideas; suggest how to connect to CB for equivalent balance?
<o:p> </o:p>
Many thanks.
I’ve just finished electrician A-grade. Someone is built the new 2 house (front and back) and asked me for information as they will supply parts and I’ll do the work. Since I’ve got hand over from my master as he is oversea for 5 months holiday, he will approve when he’s back. I’ve asked around but still need some advice. This is how I would do:
<o:p> </o:p>
For back house, 3-phase underground cable from the Pit to the electrical meter is 5 meter, so SDI cable would be 16mm2; 3 x 7meters of white-red SDI cable and 7 meter of white-black SDI cable. Front house, 240V 2 x 7m white-red and white-black cable. Is this correct? Can I make a loop before the supply meter to save front house cable? These will run under 2 x 70mm orange conduit, 600mm deep for 2 houses,
<o:p> </o:p>
Front house, from electrical meter to switchboard is 20m, same SDI 16mm2 cable, so 2x20 m white-red and white-black cable. Back house is 40m, so 3x40m white-red and 40m white-black SDI cable. Still run with 70mm orange conduit. Can I use 3-phase PCV orange cable, 4core and earth 10mm2 for the back house?
<o:p> </o:p>
If I run out of white-black SDI cable, can I use white-red SDI cable instead?
Should cable insert into conduit then put underground OR conduit first then pull cable later? I will ask someone to inspect the conduit before fill the soil.
<o:p> </o:p>
Back house, they will have 1 small (2.5kW) and 1 big (7.1kW) air conditioning, can I use 2.5mm2 cable to connect or has to be 4mm2, 1 phase each connection?
<o:p> </o:p>
Front house is ok as only 1 phase, but back house is a bit complicate. Do you have any ideas; suggest how to connect to CB for equivalent balance?
<o:p> </o:p>
Many thanks.