PDA

View Full Version : Help needed with a New Deck



freeplay
12th October 2007, 08:08 PM
Howdy all.

My project will be a new deck 10m x 5m freestanding.
It will be butting up against a pool on the 10m side, however it will not be fixed to the pool.
I would like the decking boards to run towards the pool edge ( 90 degrees to pool face ).

One end of the deck will be 3m above ground and the other end will be approx 30cm off the ground. ( from bottom of the bearers ).

Stumps will be set into concrete.

My question is, how far should my stump centers be? and will 100 x 100 stumps be ok.

regards
freeplay

builderwally
12th October 2007, 09:36 PM
G'day freeplay

The span between your stumps should not exceed 1500mm

Your bearer spacing will depend on the size of your joists
100 x 50 depending if its pine should not exceed 1800 but that may now have changed to 1500mm someone in the forum will confirm this

And yes 100 x 100 for your stump is sufficient BUT it is a bit worrying that one end is 3m high the height at this end may need diagonal bracing back to another stump

Hope i helped in anyway:U

freeplay
12th October 2007, 10:20 PM
What would I need to do in order to make my stump span 2500 apart.

Yonnee
12th October 2007, 10:53 PM
What would I need to do in order to make my stump span 2500 apart.

Depends which way...

If the 2500mm is along the bearer, you'll need much bigger bearers to span that gap and still provide the support needed. If the 2500mm gap is between bearers, then your joists will have to be as big if not bigger than your bearers!!

You'd just about have to build your deck's structural framework from Galvanized steel I-beam.

Usually, the maximum is around 1800mm for bearer span for 100x100 timber bearers, and 1500mm for joist span using 90x45 F7 joists. But this can also depend on the type of timber used.

Burnsy
12th October 2007, 10:58 PM
What would I need to do in order to make my stump span 2500 apart.

A floor load width of 4800 would require bearers of 2/290x45 to have a span of 2300 if the deck was over 1m off the ground. To have the same distance between your bearers (2300) you would need 120 x 45 joists at 450 centres.

Much cheaper to go with more posts and smaller joists and bearers.

freeplay
13th October 2007, 01:24 AM
ok
so if I go back to the two million stump option... do these roughs look right?
57763
57764
57765

I think i'm on the right track.
but I would appreciate all input.

Burnsy
13th October 2007, 02:10 AM
At your current spacing of posts at 1500mm you will need to use 2 170x45mm sticks for each bearer, and buy them as single lengths of 4.8m, don't join them.

With your joist spacing being over 1700mm and your length requirement meaning you can't go single span, you will need to use 120 x 45 at 450mm centres. This size joist would actually allow you to span out to 2300mm with 450mm centres with up to 400mm cantilever on the ends. This means you could drop off two sets of bearers and set your 5 rows up at 400mm 2700mm 5000mm 7300mm and 9600mm.

Use the longest lengths of timber you can and avoid joins where possible.

This is all from AS1684.2

oohsam
13th October 2007, 02:17 AM
That looks good. However you'd want to ensure the side where the posts are 3m high that they are stable. How far down are your holes going to be?. I would make sure they are nice and deep and put plenty of cement in them for support, extra bracing wont hurt either.
I probalby over do the support on the decking, but I'd rather have it rock solid than wobble.

What size joists are you using?>
I recentl built a deck with 40 stumps in total, but it was not high off the ground, your plan looks pretty much spot on.
With the last 2 bearers (the right most), you will not have the third row to nail your deck boards in. You may want to try and move the row in a little so you have enough bearer to put the joist on. Just an observation..
With mine, we had the same issue, but we stopped the row of stumps half way, and started a new row 50mm out. Works fine.
Cheers.

pawnhead
13th October 2007, 10:02 AM
At your current spacing of posts at 1500mm you will need to use 2 170x45mm sticks for each bearer, and buy them as single lengths of 4.8m, don't join them.Are you sure that's right. :? It sounds like overkill to me. I'd just use 150x75mm F14 bearers. They'll easily span half his width, so you'd only need one row of piers in the guts. Cheaper than F7 TP, and no poison injected in it either. (a lot of people don't like TP anymore) And $aving a whole row of footings, posts, and sweat.
With your joist spacing being over 1700mm and your length requirement meaning you can't go single span, you will need to use 120 x 45 at 450mm centres. This size joist would actually allow you to span out to 2300mm with 450mm centres with up to 400mm cantilever on the ends. This means you could drop off two sets of bearers and set your 5 rows up at 400mm 2700mm 5000mm 7300mm and 9600mm.

Use the longest lengths of timber you can and avoid joins where possible.

This is all from AS1684.2That still only gets him to 10m, and he needs 10.8. I wouldn't be putting a cantilever on the end either. It's way up in the air, so I'd be putting my posts at the end, and continuing them up for a nice solid handrail. And 120x45 is an odd size that would have to be milled. You'd have to use a 140x45.
I'd use six rows (5 bays) @ 2.16m for each bay. Then I'd use continuous 100x50 F14 joists @ 450 crs. It would end up being much cheaper with all those lineal metres of joist.

Span tables:
http://www.fordtimbers.com.au/dpr_span_tables.htm
Hwd Pricing :
http://www.barrenjoeytimber.com.au/price.cfm?CatID=8
TP Pricing:
http://www.barrenjoeytimber.com.au/price.cfm?CatID=5
Shop around in your area and you may get a better price, especially for a reasonably large single order.

Edit: I'd also buy a roll of Alcor, and use it as a bearer capping, turned down (on a 45 degree angle as a drip groove) over the edges. And I'd buy some rolls of plastic joist capping for the joists. The extra time and expense is worth the investment for a lifetime without rot in the sub structure, especially since it's around a pool.

Edit 2: After a bit more thought, you can't get a continuous joist with five bays, so it would be better to put your bearer spacing @ 2.050 crs, so you can use standard 4.2m length joists with no waste. This makes the last span about 2.525, and I'd use a single span 150x38 or 150x50 (or 125x50 if you can get it) for that. :2tsup:

freeplay
13th October 2007, 11:53 AM
MMM,

Well now you guys are getting all technical on me.
I went to the local library this morning and got Allan staines book.

My size can be flexible.. around 4m - 5m x 9m - 11m
One half, approx 4m x 4m I am looking as using the underneath to house
my pool filter and garden tools etc..
So I am looking at trying to have as little piers as posible in that area.

I don't mind paying a little extra to have more underneath working area.

I'm also not sure if Gal pipe posts would be better than wood stumps.

appreciate all the help

pawnhead
13th October 2007, 12:37 PM
One half, approx 4m x 4m I am looking as using the underneath to house
my pool filter and garden tools etc..
So I am looking at trying to have as little piers as posible in that area.I wouldn't go across it in a single span, or you'd have to use a big heavy galvanised piece of steel, or a heavy, engineered stick of timber. If you follow my layout, then you'll have an area under one half of your deck, that's 4.5m square, with just one post in the middle. The other half will be 4.5m x 5.3m, with two posts.

I'm also not sure if Gal pipe posts would be better than wood stumps.I wouldn't be casting the posts into the concrete. There's more chance of rot than mounting them in brackets.
I'm not sure if Unipiers (http://www.steelselect.com/products/download.php?id=684/) are suitable for exposed decks, but you could make inquiries.

What sort of handrail are you contemplating, and will it be integrated with the supporting posts?

freeplay
13th October 2007, 02:46 PM
If you follow my layout, then you'll have an area under one half of your deck, that's 4.5m square, with just one post in the middle. The other half will be 4.5m x 5.3m, with two posts.


Are you suggesting that i put the posts with 2200 centres?
Or did I not understand your layout?

Burnsy
14th October 2007, 03:01 PM
Are you sure that's right. :? It sounds like overkill to me.

Yep straight out of AS 1684.2, Table 49 - Deck Bearers more than 1m off the ground for a floor load width of 4800 using single span. Joist specs are off Table 50 - Deck joists more than 1m off the ground.

bpj1968
14th October 2007, 03:28 PM
Floor load width (FLW) of 4800 means that his bearers will be 4800 apart. i.e. FLW is 1/2 the distance to the next bearer, either side of the bearer. 2400 (one side) +2400 (other side)

Have a read of Allan Staines book and figure out different combinations. At present you are digging 28 holes. 28 loads of concrete, 28 stirrups etc.

pawnhead
14th October 2007, 06:01 PM
Yep straight out of AS 1684.2, Table 49 - Deck Bearers more than 1m off the ground for a floor load width of 4800 using single span. Joist specs are off Table 50 - Deck joists more than 1m off the ground.Yeh, I was looking at floor load tables which were alright in the old days. They've toughened up a lot since a few decks have collapsed.

What does the code say about F14 or its equivalent? e.g.100x50 joists.
And what sized continuous F14 bearer would he need to span half the width of 4.5m?
It would be good if he could eliminate a row of piers and just have one row in the guts I reckon.

Burnsy
14th October 2007, 06:47 PM
Sorry, seems I was miss reading the table in regard to FLW.
Here are the correct figures.

At your current spacing of posts at 1500mm you will need to use 2 120x45mm sticks for each bearer (this is based on FLW of 2400), and buy them as single lengths of 4.8m, don't join them.

With a joist spacing of 1800mm or less, you can use 90 x 45 at 450mm centres. This is based on continuous spans. With single span this would be reduced down to 1500mm.

freeplay
14th October 2007, 08:10 PM
Have a read of Allan Staines book and figure out different combinations. At present you are digging 28 holes. 28 loads of concrete, 28 stirrups etc.

I have a copy of the book...... however I'm a novice.

The building directions are straight forward.... I sure I can build it with no problems, but the stumps have me stumped.

The tables are double dutch to me.....and I sure 28 post must be overkill.

So I looking for help. on a better setup than 28 stumps.

bpj1968
15th October 2007, 11:01 AM
To give an idea of how few posts you can have

The first three photos are of my deck.
Photo 1 Steel posts and bearers. 100x100 posts and bearers 6 m long. they were 3.2, 3.6 and 4.2 apart Height was about 3 metres above ground

Photo 2 Joists were 190x 45 TP for the main part.
Photo 3 I also had 240 x 45 for the 4.2 metre span.

photo 4 and 5 are of my old deck. (The brown fence in the foreground was not connected

4 posts 100x100. ledger bolted to wall of house

Can't remeber the exact sizes but were simialr to
Beareer were 2/240x45
Joists 190x45

That deck was 3.6 x 9.0m and 3 metres off the ground. Bracing was by metal strap across the top of the joists from corner to corner. I was suprised how rock solid it was with that and no decking.

brynk
18th October 2007, 10:46 PM
gday freeplay

the first thing to consider in your design is where are you? this is required because it will affect what code & span tables you need to use if you are designing to 1684. this aside, you can use cantilevers to cut down the number posts required. from my (slightly out of date) span tables, working from your pool to the outer edge of your deck...

(using unseasoned f14 hardwood for bearers, 125x75)
pool -> 500 -> post -> 1750 -> post -> 1750 -> post -> 500 canti -> edge of deck

(using seasoned f7 treated pine for bearers, 2x 140x45)
pool -> 500 -> post -> 1750 -> post -> 1750 -> post -> 500 canti -> edge of deck

(now the joists - using unseasoned f14 hardwood 150x50, or 140x45 f7 treated pine)
edge -> 700 canti -> bearer -> 2300 -> bearer -> 2300 -> bearer -> 2300 -> bearer -> 2300 -> bearer -> 700 canti -> edge of deck

for the posts you have many options until they get over 1800 high. your worst case, the 2.4-3m high ones, require one of the following cast in a footing 600 × 600, 900 deep:
reinforced concrete 250 × 250 column
reinforced masonry 200×400 or 300x300 column
250mm dia. timber postor if you use cross-bracing on your posts (eg, from the bottom of one post to the top of an adjacent post) this option is a little more complex because you need to work out what wind-forces you have on the deck - the worst case calls for 150mm dia. timber posts with 170x45 bracing at least 400 deep

food for thought - r's brynk

freeplay
22nd October 2007, 12:55 AM
Thanks Brynk...

Bearers and joists are all clear.

The iinfo on the posts is a bit hazy.

I guess for me the 150mm timber posts on stirups would be easiest.

Although... metal posts would be a lot easier in concrete..... but I don't have the tools or skills for welding brackets on the top to hold the bearers. If i did go metal... what size post would you suggest?

brynk
22nd October 2007, 10:15 AM
as you can see & probably have a gut-feeling that the columns/piers are overkill. this is because in this instance you are looking at the 'no bracing' option, and therefore racking (or raking) forces must be dealt with accordingly. hold a pencil in your fist to help you envisage - burrow it in a lot (say, 30% of overall length) and push from the side against the top - this represents a deep footing with a wind (or other lateral) force acting upon it;

now repeat the process with the pencil only buried 10%. it doesn't matter how strong your column is, if there is nothing other than the footing to resist that racking force then the structure will be insufficient (the force will be transferred through the column acting as a long lever, onto the footing). this is where the bracing comes in - the goal is to add members to form an X-shape from the base of the column to the top of the adjacent column - this resists that force before it reaches your footings. that way your footings only need to hold the combined structural weight up, not stop it from tipping over

when working out post sizes & bracing requirements you have two options -
1) build the footings, columns & bracing specified in the worst-case scenario (that was the 150mm dia., 400 deep one i mentioned) or
2) use the code to determine your wind category based on where you are; then work out the aspect of your new deck & the surface area the structure exposes to the prevailing winds (ie, which way the high end faces); now with this combined knowledge look up the strength requirements in the table based on the area in the country, aspect, type of timber & joints being used; finally, work out a footing & post design that meets the strength requirements - if your soil classification is not covered by the timber framing code (ie, you are in sand or highly reactive clay) then the footings will need to be determined from the footings & foundation code, as2870... :o

i agree that in this situation a steel-reinforced concrete footing is the best option, especially because there is a 3m high wall with water splashing over all the time. it's gunna be wet & muddy at the base of that wall & around the base of your columns - it's also sloping down hill - a good hunk of conc. buried deeply will do wonders for your stress levels :wink: - timber cast directly into concrete will be a durability issue especially with so much water around. for that timber you would need to be looking at something that can resist the wet-rot, structural treated pine or a hardwood with natural resistance. or concrete, steel or masonry - whatever you use water will get there & you will need to drain it

standard post-stirrups will be insufficient unless your columns are heavily braced. it may pay to look at the cyclone-rated stirrups (which are U-shaped pieces of folded flat-steel, not the ones that are a tack welded tube to the piece of tin sheet). you can buy one which is set into the concrete 300, with a 300 long attachment area sticking up out of the footing to fix off your posts. http://www.pryda.com.au/catalog.php?sectionid=20&type=Post%20Anchors

the code allows you to use steel to a certain height but beyond that, if you don't have a structural engineer to counter-sign then your approval won't even get looked at!

r's brynk

pawnhead
22nd October 2007, 08:51 PM
Some good information there brynk. :2tsup:

oohsam
23rd October 2007, 12:03 AM
28 stumps too much????
I had 40 and it was ok!!....Just hire a post hole digger for a day. It will do your 28 holes with no trouble, will cost ya 90 bux..then all u gotta do is cut post, put in brick, fill with cement and back fill...done and done!
bolt some bearers, nail some joists and you've got your subframe in 2 days work, maybe 3.

freeplay
23rd October 2007, 10:04 PM
brynk...wow... thanks for all the great info.
The "High Wind Post Anchors" might be the way to go i think. I agree that putting timber posts straight into concrete in my situation would only cause more work later on in life.
The anchors posts come in a 125mm size...do you think that will be ok?
oohsam - Hole digging and concrete mixing are not an issue for me. ( I have access to a mixer and a Dingo with an auger )

Some bracing is also not a problem... I had always intended to slat the sides anyway... so I will brace the 10m side and brace 1/2 the 5m side, and put a gate/door in the other 1/2. ( all pool equipment and garden tools to be stored underneath )

So the next question is: Would the 125mm hardwood posts on High Wind Post Anchors set in say 500mm or 600mm of concrete be sufficent?

freeplay
28th October 2007, 08:14 PM
Would the 125mm hardwood posts on High Wind Post Anchors set in say 500mm or 600mm of concrete be sufficent?<!-- / message -->

brynk
29th October 2007, 04:55 PM
gday freeplay

if you want to use the option of square posts on high-wind anchors you will probably still need column bracing. as to whether they will suffice or not, type of & how deep your footings need to be, the size of the bracing required, you still need to do the following: (imagining your deck is a giant umbrella on a windy day)
use the code (as 1170.2) to determine your wind category based on where you arenow switching back to the timber framing code (as 1684.2 or as1684.3 if you are in a high-wind area)
then work out the aspect of your new deck & the surface area the structure exposes to the prevailing winds (ie, which way the open ends face)
now with this combined knowledge look up the bracing and uplift capacity requirements in the table
work out a footing & post design that meets the bracing strength requirements
finally, check the footing design to see if it meets the minimum bearing capacity - ie, how much downward force is flowing into this footing from the weight of the deck & the people using it (as opposed to the uplift restraint capacity described above) if the bearing capacity is insufficient then up the design until both the bearing, uplift and bracing capacities are metif your soil classification is not covered by the timber framing code (ie, you are in sand or highly reactive clay) then the footings will need to be determined from the footings & foundation code, as2870... find out your soil classification from your house plans;

as to whether the high-wind anchors in the pryda catalogue are sufficient? given enough posts they would be! whether the minimum number of posts identified in the earlier span-design is sufficient or not will depend on the result of the above wind calculations, bearing calculations, bracing restraint calculations

can i suggest you obtain a copy of the code - if yer lucky you could buy one from a tafe or technical institute bookstore for cheaper than you could at standards australia; before buying there you might even be able to look it up in the library at said institute - that way you could have a look at the code itself and decide if you will spend the money & design it yourself or spend the money on an engineer or a builder instead! you can still engage either of these to do you a design without having them have anything to do with the construction, granted your project does not require development approval ofcourse :wink:

r's brynk